I have been toying with multimeters on cables carrying currents I know the ratings of.

If we are out in the field, is it safe to use them on exposed cables we don't know the rating of?
 
what is the safe voltage rating of your meter?
if it allows 400v or more then you are ok unless you are in a place with HV cables.
 
It depends on quite what you are doing.

  1. If this is general LV cables that might include the supply to an installation then your multimeter has to be CAT-IV rated to at least the highest operating voltage you might expect to see.
  2. For "proving dead" there are so many ways you can go wrong with a multimeter and end up dead yourself it is not worth it. Get a voltage tester!
  3. If using a multimeter for current measurement in a power system is just asking for a blown fuse due to more than expected or switch-on surges, so really you should use a clamp meter for that rated to highest expected current (domestic and light commercial what would be 100A in most cases, but other cases you might need to kA).
  4. For voltage measurement you have to allow for the ~10M impedance of a typical multimeter, so it can see capacitively coupled voltage where no real power/current is present. It is telling you the truth in a sense, but for power circuits that "truth" might be quite misleading. Again a voltage tester that draws a few mA to light a LED is more meaningful in many cases.
  5. Having said all of the above, for medium resistance (few ohms to hundreds of kOhm) it covers what a Megger/MFT/IR tester lacks, as well as other aspects like very low current/voltage, diode check, and sometimes frequency/capacitance/etc so it can still be useful so long as you understand the above points.
 
I would just add that if you have any MV/HV cables or circuits you need to be VERY careful about how you check stuff.

I remember reading a report from the USA from a couple of years ago on deaths and injuries from electrical accidents and it had examples where a multimeter was involved. In some cases it was down to a mistake in its use (e.g. testing for AC volts on DC range and seeing little or nothing) and in the others it was due to the meter being inadequately rated and exploding in the face of the tester (e.g. checking for volts on current range and no suitable HRC fuse in the meter or probes).

In one of those cases it was not a cheapo eBay special but a proper CAT-IV Fluke meter, but the guy was checking continuity on a 4.16kV motor that was accidentally energised and the meter was not safe at that sort of voltage & fault current.
 
The original question is so abstract that the answer really has to be "no". So many caveats have to be added to make it safe.
In particular, there are more suitable tools for testing exposed cables.
 
Not the perfect tool for the job but it can be useful as long as its got all of the protections, I do find separate tools better though, if I want to know the voltage I just grab the voltmeter and for current the clamp or ammeter.

Few years ago I bought one of those cheap yellow multimeters to play around with, and tried measuring mains voltage, the moment I probed the live contact of the socket there was a short and the multimeter exploded, I wasn't holding it so nothing happened to me. I had it on the right scale and everything, I guess it was just a terrible unit that wasn't meant to test mains even though it claimed it could.

From that moment on I just use my multimeter to measure low voltage DC and resistors and an analogue voltmeter with a series of tiny light bulbs (load) for mains, it can measure up to 500V so enough for both single and three-phase power.
 

Reply to Multimeters, Can we use them on Random exposed cables. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello. I'll apologize to start with as due to my lack of knowledge on the matter I'm likely to waffle a bit and call everything by the wrong name...
Replies
16
Views
2K
Hi There Just a quick one, I'm wondering what's everyone's thoughts on this are. A subby has clipped a cable to a plaster board ceiling using 3m...
Replies
8
Views
690
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
748
Trying to find an armoured cable behind plasterboard and studding. It was used to supply power from the house but has been disconnected Can...
Replies
2
Views
426
We are looking for a distribution board to provide 3 * 160A three-phase feeds, but they are basically redundant supply path options so max total...
Replies
4
Views
284

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock