Hi, there is 4 in total on the plans two in front room one in main bed and one in family room, how will I know which is to be the master? Would I be installing the master one?1st one is master, usually installed by BT. then just daisy chain slaves from there. you should not have more than 4 slaves from a master.
no the master is installed by BT, if you had read my earlier post.Hi, there is 4 in total on the plans two in front room one in main bed and one in family room, how will I know which is to be the master? Would I be installing the master one?
I did read your earlier post.no the master is installed by BT, if you had read my earlier post.
i would think so. you only need to wire pins 2 and 5. leave cable at master point and connect once master is installed.I did read your earlier post.
im assuming bt wont have installed the master by the time I arrive so how do I go about wiring the ones on the plans do I run the cables back to one I assume will be the master socket?
Ok thank you for your help. It’s only first fix stage so I’ll just be running all the cabling not connecting anything up at this stage, I’ll daisy chain from what I’ll judge as being the master maybe a front room one I suppose?i would think so. you only need to wire pins 2 and 5. leave cable at master point and connect once master is installed.
Thank you very much. Still unsure as to how I’ll determine which of the 4 bt points on the plans will be the master if I finish first fixing and bt decide to put the master somewhere else I’ll be screwedYou should wire 2 3 and 5 if you want the bells to ring. It is good practice to wire all six if using 3 pair cable to CW 1308.
There is no limit to the number of sockets you can wire in but the old rule was that the maximum REN of the phones plugged in should not exceed 4. REN is ringer equivalent number and used to be used when phones had 4 k ohm bells to limit the amount of current drawn from the exchange. With modern phones I do not really think it matters too much now.
Remember that you should use secondary sockets for everything except the Master which should be provided by BT or the line supplier.
A secondary socket does not have a ringing capacitor, opt out of service resistor or a lightening suppressor.
You or the client should tell BT where to put the flaming Master Socket. The standard price for a new BT line does not vary with the length of cable runThank you very much. Still unsure as to how I’ll determine which of the 4 bt points on the plans will be the master if I finish first fixing and bt decide to put the master somewhere else I’ll be screwed
Thank you very much. Still unsure as to how I’ll determine which of the 4 bt points on the plans will be the master if I finish first fixing and bt decide to put the master somewhere else I’ll be screwed
You or the client should tell BT where to put the flaming Master Socket. The standard price for a new BT line does not vary with the length of cable run
Great thank youYou or the client should tell BT where to put the flaming Master Socket. The standard price for a new BT line does not vary with the length of cable run
1st one is master, usually installed by BT. then just daisy chain slaves from there. you should not have more than 4 slaves from a master.
Ok great thanks. I’m starting first fix tomorrow so I’ll speak to the builder and/or bt too.BT will put the master wherever you ask them to, it makes sense to have arranged it with them beforehand to establish what is required from their point of view.
Remember BT will stop installing copper services soon in favour of fibre services.
If you don't arrange anything with BT you may find that they come in and run a surface cable around the inside of the property!
[automerge]1592773379[/automerge]
It doesn't, but the BT operatives are expected to complete a new service install in a specific time regardless of where it is being installed or how much work is involved so they tend to work as quickly as possible (and to a low standard)
That’s a good point about being able to use either end of the radial and I agree about it being old fashioned, it must be an old guy architect who drew the plans up.If you run a radial between all the secondary’s, there’s a choice of two that can be the master.... one at each end.
kind of old fashioned having a load of phone points. I bet the homeowner ends up with DECT phones and a bunch of empty phone sockets
Suggest have a look around to see how BT has installed nearby properties. Make the master say the nearest to the road. Then radial out from there. Copper is going to be around for a very long time. I have just done a similar and used Cat5 as i carry it anyway.
cheers
P&S
Great thank you.Suggest have a look around to see how BT has installed nearby properties. Make the master say the nearest to the road. Then radial out from there. Copper is going to be around for a very long time. I have just done a similar and used Cat5 as i carry it anyway.
cheers
P&S
It is now only 2 & 5 that are used the wiring of terminal 3 is known to cause interference and affect ADSL broadband speed and bandwidth while older phones may need terminal 3 connected newer equipment does not. With multi pair cables it is actually better to connect any spare cores down to earth than connect them to the socket again to suppress interference that may affect the broadbandYou should wire 2 3 and 5 if you want the bells to ring. It is good practice to wire all six if using 3 pair cable to CW 1308.
There is no limit to the number of sockets you can wire in but the old rule was that the maximum REN of the phones plugged in should not exceed 4. REN is ringer equivalent number and used to be used when phones had 4 k ohm bells to limit the amount of current drawn from the exchange. With modern phones I do not really think it matters too much now.
Remember that you should use secondary sockets for everything except the Master which should be provided by BT or the line supplier.
A secondary socket does not have a ringing capacitor, opt out of service resistor or a lightening suppressor.
HA, HA, not a hope in hell. You can double that and still be hoping. There are not enough engineers in the world to do that, even if the money was available (which it isn't)'very long time' is a bit of a stretch when the current target is for the copper network to be taken out of service in between 5 and 7 years time.
I presume you mean a true earth and not one connected to the household electrical system?With multi pair cables it is actually better to connect any spare cores down to earth than connect them to the socket again to suppress interference that may affect the broadband
Actually, the master can be at any of the points. You can wire two wires into a standard punchdown terminal - so can run extensions off in two directions.If you run a radial between all the secondary’s, there’s a choice of two that can be the master.... one at each end.
But as a late friend of mine was fond of saying, better looking at it than for it. It's easy to not use sockets that are there, it's "a lot harder" plugging into a socket you want to use that isn't there.kind of old fashioned having a load of phone points. I bet the homeowner ends up with DECT phones and a bunch of empty phone sockets
As already said, that's just pie in the sky thinking - not a snowball's chance in hell of it actually happening in that timescale. If they were serious about it, they've be pushing fibre right now - but as it is, they still have pricing (e.g. for FTTPoD, that's on demand) that seem designed to avoid anyone taking them up on it.'very long time' is a bit of a stretch when the current target is for the copper network to be taken out of service in between 5 and 7 years time.
No. Current designs of filter plate split out the DSL signal before filtering the voice signal and splitting out the ringer line. So it's safe to wire pin 3.It is now only 2 & 5 that are used the wiring of terminal 3 is known to cause interference and affect ADSL broadband speed
Doesn't have to be those, many older designs also have terminals for the A&B wires. One way of doing it is to use (e.g.) the green/white pair for the DSL and link that pair behind the extension sockets until you get to the one where you want your modem - then you fit a BT+RJ11 socket and don't take the DSL signal any further.If BT fit an NTE5c+VDSL Mk4 filter it is possible to wire from the filter to an RJ11 extension socket or module for a VDSL hub / router to be located away from the NTE5c ( master ) socket at a more convenient location.
Actually, the master can be at any of the points. You can wire two wires into a standard punchdown terminal - so can run extensions off in two directions.
But as a late friend of mine was fond of saying, better looking at it than for it. It's easy to not use sockets that are there, it's "a lot harder" plugging into a socket you want to use that isn't there.
No. Current designs of filter plate split out the DSL signal before filtering the voice signal and splitting out the ringer line. So it's safe to wire pin 3.
Doesn't have to be those, many older designs also have terminals for the A&B wires. One way of doing it is to use (e.g.) the green/white pair for the DSL and link that pair behind the extension sockets until you get to the one where you want your modem - then you fit a BT+RJ11 socket and don't take the DSL signal any further.
At my parents house when I was still living there "some years ago" we added extension sockets (as well as more mains sockets, aerial etc) as we redecorated. I put a 201C box under the stairs, routed the incoming line down to it (honestly, the master socket moved all by itself), and then radially wired out to the extensions. I put a filter on the master socket, and only ran an unfiltered line up to my back room where I had the router.
Its a really good point. Commercial clients who have enjoyed Fibre direct for decades have been able to get BT to route the fibre directly into a comms room or computer room, where power is available. Obviously ( or possibly not for Joe Public) fibre has to be lit and this needs power. Traditionally with Fibre cables there is no power within the cable, it has to be provided locally. More work for sparkies, lolI had fibre to the house installed yesterday and it works really well. However there is a box the fibre terminates into then a patch lead to the router both need a 13A socket and all the old copper has been retained as the exchange is not fibre ready for the telephone part of it. I am just glad that it is all in a cupboard and not in a corner of the living room. On that basis if I was wiring a new house now I would try and put the master socket in a cupboard.
I worked for BT for over 20 years on and off, started in 1986 when BT first started out rolling out fibre and going digital, my job then in 1986, was getting it into MNCs and Cellular Towers. When the big bang came along we simply could not keep up with demand and we had 240,000 employees. Over the years watched BT wrestle with government, wrestle with its balance sheet and today it does not have two half pennies to rub together. Getting fibre to a street cabinet was challenging but now we do have "superfast broadband" - great stuff. Getting fibre to each home is several orders of magnitude harder, more expensive and costly.... Good Luck BTAgree with Plugsandsparks.
No organisation or Government has got close to meeting a target they've set or has been set for them.
Not so Smart Meters being the best example.
High speed broadband for everyone (or the majority) in the U.K, not a chance.
Elun Misk with have his Broadband global network of tens of thousands of satellites up and running his before the U.K get's all Fibre.
Just hope they don't catch fire like his cars do.
Strange how the Yanks don't trust the Chinese and Huawei, but will be trusting Misk with his background.
TBH it was difficult to get any info from BT they were working on the basis that I was a stupid customer and their wonderful engineer would fix every thing, I didn't even know if I was getting fibre to the cabinet or to the home until the guy arrived. Then there was the issue of an extra socket, I gave him an extension and wired a socket last night, no problem to a spark but for Joe Public? The next issue was that he was not allowed in the attic due to covid!! so he was going to clip a cable all around the house, so I ended up in the attic pulling the fibre in for him, at least he was flexible and would come and go.Its a really good point. Commercial clients who have enjoyed Fibre direct for decades have been able to get BT to route the fibre directly into a comms room or computer room, where power is available. Obviously ( or possibly not for Joe Public) fibre has to be lit and this needs power. Traditionally with Fibre cables there is no power within the cable, it has to be provided locally. More work for sparkies, lol
Its a really good point. Commercial clients who have enjoyed Fibre direct for decades have been able to get BT to route the fibre directly into a comms room or computer room, where power is available. Obviously ( or possibly not for Joe Public) fibre has to be lit and this needs power. Traditionally with Fibre cables there is no power within the cable, it has to be provided locally. More work for sparkies, lol
BT are using plastic fibre for the overheads not sure what UG fibre they are usingso would have thought BT would proceed with a glass only solution with power provided locally. Just a guess but that is how it has been done to date.
The front part will take two wires - or at least all the older designs before the current POS took two wires in each terminal. Two wires in a terminal = means to run two radials, a.k.a. having the master in the middle of a run. Otherwise, there's always 3 way jellies in the back of the box as an option !The NTE5 master HAS to be the first socket on the incoming line as removal of the lower part or in the newer NTE5c the front part of the socket isolates the extension wiring for testing of the incoming line. The base part of the socket is the test point for the incoming line