Relating to an earlier discussion of using common multicore cable for multiple circuits ;; their isn't anything wrong with this as long as the insulation is rated to the highest voltage of all the circuits contained in the cable and that it is possible to locally isolate all circuits at one point, its slighty of track here from domestic but this is common in servo cables and machinery... as long as screening etc are taken into account..

A lot of motors run one multicore cable that house both the motor feed and other control based wiring like thermal trip or force fed fan.... again its not so common in installation wiring as it has no functional advantage usually.

I think the op or his 'Mate' who has said this is getting confused with generated Eddie currents when not running all the phases of say a 3 phase load through the same conduit set or glanding points in a metal plate - which can give way to high heat generation and overheating of cables
 
2 circuits in one cable would mean two point of isolation via two MCB's etc. Safe isolation for the cable can not be obtained from a single point. It must be against the regs?

by your reasoning every 3 phase motorway lighting installation in the country does not comply.
 
Arnt you allowed 2single phase circuits in the one conduit???? A guy said a no no but 3ph yes. I diss missed from the off as I believe you can.

Is is this a good practice thing.

you need to stop hanging out with morons.
or at the very least stop repeating their demented claptrap so that it doesnt make you look a bit of a clutz as well.

;-)
 
yes you can run them in conduit providing there is adequate room and derating and conduit fill rules are followed.
not sure about uk regs but in the US. you cannot run communications cabling in the same conduit as power conductors.(induced currents can cause unwanted error signals and compromise safety devices on automated equipment)
 
by your reasoning every 3 phase motorway lighting installation in the country does not comply.

That wouldn't be a good rebut Biff .. since when did the street lighting come under BS7671... not critising the point you make but poor example used ;)
 
yes you can run them in conduit providing there is adequate room and derating and conduit fill rules are followed.
not sure about uk regs but in the US. you cannot run communications cabling in the same conduit as power conductors.(induced currents can cause unwanted error signals and compromise safety devices on automated equipment)
Same here fella, we have rules about segregating different structures of cabling, Communications and power a big NO NO also in the UK
 
Technically you can if the comms cabling has the same voltage rating as the power cabling
 
Hmm, well the comms cabling would need to be screeded for starters and I am struggling to think of a 230 or 400 volt comms system at present, that said you may well be correct.
 
That wouldn't be a good rebut Biff .. since when did the street lighting come under BS7671... not critising the point you make but poor example used ;)

you reckon ?

every street lighting system ever built has to have its electrical elements comply with bs7671 even if other standards are to be considered during the design.
i can guarantee that with my last dollar.

and my original point is that all motorway lighting circuits use 4 core swa cables which are connected to a 3 phase source but by means of single pole devices only , so if 1 phase developes a fault the rest remains lit.
which in turn shows its acceptable to have a multi core cable with more than 1 OCPD for its cores.
which is why i quoted pauls post.

it was actually a very good example , wise guy.
;-)
 
you reckon ?

every street lighting system ever built has to have its electrical elements comply with bs7671 even if other standards are to be considered during the design.
i can guarantee that with my last dollar.

and my original point is that all motorway lighting circuits use 4 core swa cables which are connected to a 3 phase source but by means of single pole devices only , so if 1 phase developes a fault the rest remains lit.
which in turn shows its acceptable to have a multi core cable with more than 1 OCPD for its cores.
which is why i quoted pauls post.

it was actually a very good example , wise guy.
;-)

I did use a similar argument earlier and yes it may well comply to BS7671 as its own BS catagory is likely to be intertwined with BS7671 pretty much as BS 60204-1 is which i usually work under a lot otherwise they would conflict at any mutual crossover points... i just meant using an example that has its own BS catagory can be misleading and as far as i know it still needs to have a device that disconnects all line conductors if not just for maintenance...

Edit - 559.6.2.3
 
you reckon ?

every street lighting system ever built has to have its electrical elements comply with bs7671 even if other standards are to be considered during the design.
i can guarantee that with my last dollar.

and my original point is that all motorway lighting circuits use 4 core swa cables which are connected to a 3 phase source but by means of single pole devices only , so if 1 phase developes a fault the rest remains lit.
which in turn shows its acceptable to have a multi core cable with more than 1 OCPD for its cores.
which is why i quoted pauls post.

it was actually a very good example , wise guy.
;-)

I'd have to look it up in BS7671, but all the street lighting systems (not motorways) on our projects have been supplied at source via a 4 pole breaker, Quite often seen sections/runs of motorway lighting out in the UK though, so it seems they had been supplied by a multi phase breaker too. In fact it's quite rare to see, say every 3rd single motorway light out (eg, a single phase gone down).

I'm just going by my own observations here, you may well be right on the methods now being used for motorway lighting...
 