S Shpark ~ Aug 26, 2022 #1 If changing a socket front front or light is a minor works required and would you test the circuit
timhoward ~ Broke Internet Esteemed Arms Aug 26, 2022 #2 This might help you: Views on Minor Works Certs - in - UK Electrical Forum , Views on Minor Works Certs, UK Electrical Forum, ElectriciansForums.net Est.2006 | Free Electrical Advice Forum and page_number. www.electriciansforums.net
This might help you: Views on Minor Works Certs - in - UK Electrical Forum , Views on Minor Works Certs, UK Electrical Forum, ElectriciansForums.net Est.2006 | Free Electrical Advice Forum and page_number. www.electriciansforums.net
telectrix ~ Mentor Arms Aug 27, 2022 #3 Shpark said: If changing a socket front front or light is a minor works required and would you test the circuit Click to expand... i'd do a Zs and RCD trip test. MWC is optional.
Shpark said: If changing a socket front front or light is a minor works required and would you test the circuit Click to expand... i'd do a Zs and RCD trip test. MWC is optional.
D Dustydazzler Aug 27, 2022 #4 As above Zs before , Zs after and RCD trip time at 1 x Thats is and I move on , unless I am adding cable or altering the cable route or adding a point then I never bother with a MWC
As above Zs before , Zs after and RCD trip time at 1 x Thats is and I move on , unless I am adding cable or altering the cable route or adding a point then I never bother with a MWC
7029 dave ~ Mentor Arms Aug 27, 2022 #5 RCD might not be present in some older installations , one less test to do. Zs is a must IMO