confirm yourself.....dont take Mr. `BG fitters` word for it.....with the ever present spectre of the `upsell`.....steeped in it are these lot...
and if the Ze is high...or bobbing about...then as its distributers facility then they have a duty of care to maintain it.....so dont be fobbed of by `you`ll have to rod it`.....or some other jingle jangle like that.....
 
rule #1. if a BG so called "engineer" says its wrong, then it's probably OK...... rule #2. refer to rule#1. BG have "engineers" to shovel poo out your drains.
 
You'd have to ask UK Power networks that one. I did see whilst doing my lev 3 studies a diagram that showed an older style arrangement for TN-C-S, where they attach an earthing clamp to the sheath, then to the MET, but not quite how they did it. At the end of the day, the earth path is the same as illustrated, with the addition of bonding the lead sheath, and if the sheath is unbroken along the whole supply run as a standard TN-S, then it's a kind of belt and braces thing I suppose.

With my installation as was, there was no connection to be found anywhere on the supply sheath, and no bonding to gas or water. (Nor any connection to supply neutral, and no earth stake) No earth cables other than the CPC's of circuits ran to the earth block in the old CU, bar one that went to a second CU upstairs, and again there, there was only the CPC's to circuits. It still remains a mystery.

Most converted underground TN-S to PME cables are supplying both TN-S and TNC-S, and therefore should NOT have any sheath connection to the artificial PME neutral earth. In fact any exposed cables lead sheathing should be wrapped in an insulating amalgamating tapping.
 