Discuss need help with energy let thru data in the UK Electrical Forum area at ElectriciansForums.net
can anybody help me with reguards to the i2t (energy let through data) some manufactures provide a graph and others state a figure. im confused as to what value of I2t (energy let thru to use) for a given fault current when trying to calculate minimum cpc for fault currents <0.1s
I2t < s2k2
please can anyone help.
If the 3ka is your PSC at the supply then this will be used to look up the I2t rating of the mcb , but each manufacterer and mcb type is different so you'll need the mcb makers info.
right thankyou biff , so if my PSC at supply is 1.8kA (measured) then i would use this as my fault current when looking up the I2t on the manufactures graph.
some manufactures just supply figures for 3ka 6ka 10ka mcb rating ect (max values of i2t ) if your max PSC is only 1.8kA what figure would be used for i2t sorry if im beeing thick just confused as the data is presented in different ways.
trying to work out if a cpc has been incorectly sized. i used the adiabatic and manufactures time/current graph due to low zs and discconection time being 0.01s and it appeared fine. now when using i2t <k2s2 im not sure as to which figure i need to use for i2t if that makes any sense
Sounds challenging stuff , not usually done in such detail for regular work , is this for a college course ?
If your doing this stuff often i'd recommend bying the IEE design guide book , it gives working examples of the I2t calcs.
your right im going too deep ill just stick with the adiabatic calclations seem to work out fine
zs 0.35. i = 230/0.35 =657.14 A. k= 115. t = 0.01s (manfactures data)
so S = sqrt(657.14^x0.01) /115
= 0.57mm2 so 1.5mm2 cpc should be perfectly ok.
^^^ All that for 1.5 lol ?! wouldnt blame you if it was 185mm SWA at £200 a metre lol.
Good effort on the calcs though :)
Reply to need help with energy let thru data in the UK Electrical Forum area at ElectriciansForums.net
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Need help check that my cable calculations are correct as still new to doing them. 6A Lighting Circuit 60898 MCB Type B wiring in 1MM²/1MM² T+E...
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Hi, and thank you to anyone who's taking the time to read my question. i'm struggling with the outcome of an adiabatic equation i'm doing and...