Is neutral the correct word to use on a 2 wire TN-C-S supply coming from a single 11kv-240 volt single phase 2 terminal secondary transformer? Or would it technically be called the earthed conductor instead?
 
Look up the definitions in BS7671; Neutral, Live conductor, PEN conductor. I suppose it depends at what point, you are inspecting that conductor?
 
Last edited:
It depends what frame of reference you want to use, in terms of pure scientific definition I don't think it could be called neutral, but as far as electrical installations and bs7671 is concerned it is still the neutral
 
It's at or near earth potential but not used as a protective conductor, and it carries the load current.

If it walks like a neutral and quacks like a neutral...
 
think you made a right duck up of that spelling.
 
don't be daft. where yo going to find a right div on a bank holiday weekend?
 
This thread has veered off course and no longer neutral lol :)

As others have said, in context, it is defined as neutral by the regs. It has no potential and therefore neutral.
 