Thanks all for comments even the ones pointing out what a doughnut I was being around the sw live think because dimmers kept blowing. I got to bottom of the lighting some how that dimmer on that circuit was affecting the lighting circuit that was tripping and had the IR readings of around 0.15 on both L-E and N-E. I can't really understand why this was creating the readings I was getting as I had all conductors of circuit disconnected and all loads off
 
Is there anybody that can describe to me how this fault was occurring. For the life of me I can't see how a dimmer switch connected on one circuit could be tripping the rcd out on a different one?
 