Don't come across this very often - but I've had a CU delivered for a caravan job (not static btw), and it's been supplied with a neutral conductor from the main switch to the neutral bar! Definitely an oversight, but I've got plenty of singles cable in stock, so rather than send it back, I thought I could reuse what I have. However I've scoured the regs book, and I can't get a definitive answer as to what size this particular conductor should be. Obviously in a domestic setting it's either 16 or 25.

It's a 25A main switch with RCD and the highest the incoming current will be is 16A, so I can't see it's going to need a huge neutral conductor. I'm guessing a 4mm will do.

If there is something in the regs about this, could someone point it out to me. Cheers.
 
Make it at least as big as the incoming live cable and all will be good.
 
Incoming cable on a touring 'van will probably be only 2.5mm2, while RCD and neutral bar terminals will be designed for 25mm2 or more.
The cable selected for the link will have to be a bit bigger than 2.5mm2 to get a reliable connection, or have ferrules or lugs crimped onto the ends.
 
Thanks, I thought that's what it would likely be. Just as a note, I found the neutral cable for it, tucked separately in the packing! But its so big it doesn't fit the neutral bar terminals anyway lol. Looks like they've just bunged in a 16mm and thought "That'll do"
 
Incoming cable on a touring 'van will probably be only 2.5mm2, while RCD and neutral bar terminals will be designed for 25mm2 or more.
The cable selected for the link will have to be a bit bigger than 2.5mm2 to get a reliable connection, or have ferrules or lugs crimped onto the ends.

Terminals in a CU will be designed for 1mm upwards otherwise they wouldn't be much use in a CU.
 
Terminals in a CU will be designed for 1mm upwards otherwise they wouldn't be much use in a CU.
Those go into the MCB or RCBO terminals, which are generally somewhat smaller than those on the incomer. The terminals on the neutral bar that will accommodate cables down to 1mm2, but the one intended to terminate the link from the incomer is usually much larger.
 
Those go into the MCB or RCBO terminals, which are generally somewhat smaller than those on the incomer. The terminals on the neutral bar that will accommodate cables down to 1mm2, but the one intended to terminate the link from the incomer is usually much larger.

I can't say I've ever noticed that on the boards I fit, all the terminals are normally the same size.
 
I can't say I've ever noticed that on the boards I fit, all the terminals are normally the same size.
Very often, even on a domestic CCU, but especially in commercial DBs, one or more neutral and earth terminal in the bars will be larger than the remaining ones. Small domestic boards often have 3x 16mm² holes and the rest 10mm, one for the tri-rated tail and the others to install those pesky ovens and showers...
 

Reply to Neutral Conductor Size - Main Switch to Neutral Bar in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, Ignoring the appauling conductor terminations which I found, in the background of the photo you can see a really odd neutral tail terminated...
Replies
17
Views
2K
Greetings, I'm a EE and have installed many electrical systems but am now dealing with my first large 3PH install on our property. I'm not...
Replies
4
Views
880
Hi I've inherited a very tight space, a KMF switch and some split-con for a sub-main to try and tidy up. It's a joyous non-restrained single...
Replies
3
Views
174
Howdy DIY soldiers, first post here. My question comes down to whether it would be particularly unsafe for me to temporarily wire nut and tape a...
Replies
2
Views
1K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
412

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock