Hi I have 2 X single 3.2kw, my old oven was just plugged into a socket in my kitchen cabinet not protected by anything inline between cooker and MCB in dB box,
I'm thinking off the following, running 6mm cable from my 32a MCB to a dual appliance plate rated at 45a then the dual appliance plate will supply 2 X 13a fcu which will supply each oven. This way both ovens are protected and the cable is protected.