Hi,

Can anyone confirm if rcd protection MUST be incorporated to a new in line fan sited in the loft space above a bathroom.

I understand all circuits supplying a bathroom must be rcd protected on new installations or when altering, so have I just answered my own question??

Reason I ask is you can only hear the fan and touch a plastic grill on the ceiling, so is it really in the bathroom?

Obviously rcd protection would be better its just would involve considerably more cost for the customer due to either c unit upgrade or more wiring alterations and putting an rcd fcu in.

Thanks
 
Can u not fit RCD near the fan isolator I would certainly install and RCD to new bathroom extractor
 
Yes mate certainly could it would just mean a bit of chasing the wall and extra cost, just wanted to get my facts straight before I did potentially unnecessary work ,
 
If no part of the circuit (isolator, cables, associated lighting) are within the bathroom then RCD protection can be omitted (assuming the cables are not buried <50mm in any wall).
If you were fitting an RCD you could fit the RCD FCU in the loft, just protecting the fan itself, may be somewhat inconvenient if it trips, but since the fault would be with the fan itself you would need to get in the loft to resolve the problem.
 
And obviously if the manufacturers instructions call for a 3A fuse/isolator then a RCD FCU makes perfect sense.
 
Thanks guys, I will give the customer the choice of providing rcd fcu to cover bathroom lights and new in line fan or the cheaper option of fan isolator in lift beside new in line fan omitting rcd as all cabling in loft space.
 
Thanks guys, I will give the customer the choice of providing rcd fcu to cover bathroom lights and new in line fan or the cheaper option of fan isolator in lift beside new in line fan omitting rcd as all cabling in loft space.

I assume the fan is double insulated ?
 
Can you not fit an RCD module external to the CU on the bathroom lighting cct (presuming you have spurred of that cct?) and then you can rest easy that you have suitable additional protection to all bathroom circuits?
 
or fit a hand cranked fan. give her indoors something to do while you're in the shower.
 
And obviously if the manufacturers instructions call for a 3A fuse/isolator then a RCD FCU makes perfect sense.

Something i don't and dare say never will take any notice of!! lol!!

If the manufacturers fan needs a 3A fuse protection it should be provided by the manufacturer!! BS1361 fuses are not and never have been for the protection of appliances or equipment, they are designed only for the protection of connected cables/flex/chords, ...end of!!
 