A mate rang me up yesterday, his son has just bought a brand new house, and a brand new cooker. He rang me up to ask if it was OK to wire his cooker in, he said i have some heat resistant flex that came with it. Fine no problem get on with it. He rings back an hour later, Howard i dont know what i have done wrong but when i turn the cooker switch on, on the wall, there is a bang from the fuse box, can you come and have a look?.

So off i go, check his wiring, no problems all wired up as it should be into cooker connection outlet. Turn off cooker isolator reset RCD and MCB, switch on cooker switch, BANG. Did IR test short circuit between L-E. L-N and E-N 500Mohm. Oh dear short circuit. I noticed that the builder had put a gas outlet behind the oven, and a socket outlet at the side of the cooker connection unit. Found L-E reversal in the socket, sorted out and all is OK. I looked at the EIC from Nov2010, and compared my R1+R2 and Zs readings to the ones on the EIC, they were no where near. If they had done their testing properly this reversal would have shown up. another case of made up test results i fear. There are about 60 houses on this development, i maybe getting busy.

I know the company who did the install, and i once had an interview, but i wasn't good enough for the job.

Cheers............Howard
 