An RCD is a residual current device (RCD).
An RCBO is a residual current device (RCD).
both are RCDs
An RCBO is a residual current device (RCD).
both are RCDs
Not sure what you mean.So why do we recommend an all RCBO board and not a all RCD board?
That’s my point. Most that I’ve seen are combined devices, so do we need a new form for a board filled with AFDDRCBO’s as well as a different one for split load boards, and another one for all RCBO boards?Will AFDD's ever become the norm, or will the manufacturers take the bull by the horns and combine them?
Live/Earth includes the neutral to Earth insulation resistance, as well as the line (phase) to Earth. Live/Live is not only phase to neutral, but also between all phases, and these to the neutral.Wondering why they isn’t a Zs box to fill in,& if Connected to origin do not fill in box.
Also altered the Rcd times,now just entering the x5 trip time.
Why is there no N-E insulation reading ,& a L-L entry,which I would take to be L-N.
Just pondering these thoughts,will phone helpline next time in office,but any ideas.
RCD is a generic term. What you are describing as an "RCD" is, in fact, an RCCB (residual current circuit breaker). This is merely one type of RCD.It's probably the Aspergers kicking in, everything must be correct and in order, to me an RCD does not do the same job as an RCBO therefore should not be listed in the same way.
This is my point I don’t do an all rcbo board I do a split load rcd but I see the pros and cons of both, on the test form if it’s rcbos you will enter each rcbo reading individually normally round about the same, and then rcd covering few circuits is the same for each circuitSo why do we recommend an all RCBO board and not a all RCD board?