If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)
Wondering why they isn’t a Zs box to fill in,& if Connected to origin do not fill in box.
Also altered the Rcd times,now just entering the x5 trip time.
Why is there no N-E insulation reading ,& a L-L entry,which I would take to be L-N.
Just pondering these thoughts,will phone helpline next time in office,but any ideas.
 
onlyrequired now to enter the RCD x 5 value. L-L is there as it's now considered that N is a "live" conductor. confusing as you'd think L-L would be phase-phase on a 3 phase install.noo idea about the Zs box.
 
No N-E test then,cheers
 
You measure Ze at the origin not Zs , hence no Zs box for the origin.
N-E IR tests are covered in the L-E column.
L-E means all live conductors which includes the neutral tested to earth.
 
  • Like
Reactions: ChrisElectrical88
There’s never been a Zs box on the Domestic certificate schedule only on the non domestic. L-L Is L-N, L-E you put the lowest out of L-E or N-E. The neutral is a live conductors. The RCD box you enter the value which is required depending on what the RCD is installed for.
 
  • Like
  • Agree
Reactions: cliffed and Ian1981
And I wonder who will be the first of any of the scheme's that will bring out a form for an all RCBO board?
 
We’ve got the niceic guy coming soon any tips on how to deal with him...nice ones please .
 
Ask questions? Anything your not sure on. He will appreciate your desire to broaden your knowledge and as long as he is answering he’s not asking.

admit when you don’t know, but give the opinion at what you think may be the right answer.
 
  • Like
Reactions: DPG
We’ve got the niceic guy coming soon any tips on how to deal with him...nice ones please .
Tea, Hobnobs - preferably the plain chocolate ones.
 
They already do, the current certificates allow for any boards, you just have to fill the information In correctly.
Not on the software I have (three different) the content only mentions RCD's and the DB report also has RCD printed on the top of the from, what software do you have that allows this to be altered?
 
It's probably the Aspergers kicking in, everything must be correct and in order, to me an RCD does not do the same job as an RCBO therefore should not be listed in the same way.
 
An RCD is a residual current device (RCD).
An RCBO is a residual current device (RCD).

both are RCDs
 
So why do we recommend an all RCBO board and not a all RCD board?
 
No I am sure you don't.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

cliffed

Arms
~
Joined
Location
Worcester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Niceic cert filling in on software programme
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
43

Advert

Thread statistics

Created
cliffed,
Last reply from
Doomed,
Replies
43
Views
4,726

Advert