cliffed
2,210
700
102,788
Worcester
Wondering why they isn’t a Zs box to fill in,& if Connected to origin do not fill in box.
Also altered the Rcd times,now just entering the x5 trip time.
Why is there no N-E insulation reading ,& a L-L entry,which I would take to be L-N.
Just pondering these thoughts,will phone helpline next time in office,but any ideas.
onlyrequired now to enter the RCD x 5 value. L-L is there as it's now considered that N is a "live" conductor. confusing as you'd think L-L would be phase-phase on a 3 phase install.noo idea about the Zs box.
No N-E test then,cheers
You measure Ze at the origin not Zs , hence no Zs box for the origin.
N-E IR tests are covered in the L-E column.
L-E means all live conductors which includes the neutral tested to earth.
Reactions: ChrisElectrical88
There’s never been a Zs box on the Domestic certificate schedule only on the non domestic. L-L Is L-N, L-E you put the lowest out of L-E or N-E. The neutral is a live conductors. The RCD box you enter the value which is required depending on what the RCD is installed for.
Reactions: cliffed and Ian1981
And I wonder who will be the first of any of the scheme's that will bring out a form for an all RCBO board?
We’ve got the niceic guy coming soon any tips on how to deal with him...nice ones please .
Ask questions? Anything your not sure on. He will appreciate your desire to broaden your knowledge and as long as he is answering he’s not asking.
admit when you don’t know, but give the opinion at what you think may be the right answer.
Tea, Hobnobs - preferably the plain chocolate ones.
They already do, the current certificates allow for any boards, you just have to fill the information In correctly.
Not on the software I have (three different) the content only mentions RCD's and the DB report also has RCD printed on the top of the from, what software do you have that allows this to be altered?
It's probably the Aspergers kicking in, everything must be correct and in order, to me an RCD does not do the same job as an RCBO therefore should not be listed in the same way.
An RCD is a residual current device (RCD).
An RCBO is a residual current device (RCD).
both are RCDs
So why do we recommend an all RCBO board and not a all RCD board?
No I am sure you don't.