Yesterday discovered that the RCD had tripped in the board on our new site. Those sockets feed a hired site office cabin, and that in turn feeds a hired chemical toilet. A quick bit of investigation revealed the main reason for the trip was the commando plug/socket for the toilet had filled with rainwater, so RCD did its job.

But...when checking things out I did an IR test on the feed to the hired office and found it disturbingly low. Both L-E and N-E around 0.2M, and if I checked the individual lives by isolating circuits with the MCBs found the internal sockets (with everything unplugged and/or removed) was 0.5M for L-E, the two heaters about 1.5M, and lights about 1M.

It is dry inside, is only 10m x 3m in size, and only has four double socket outlets.

Any ideas why it is so utterly crap? For comparison I was getter marginally better IR on the water-filled toilet lead after opening and shaking out the half-cup of water it has accumulated!

It is hired so not really our business to monkey with it, but for now we are powering it off when not on site just in case :(
 
There wad a thread a few weeks back about T+E with partially conductive 'insulation'. If the fittings are dry it seems the most likely cause. Unless they have been on power while wringing wet and started to develop tracking internally.
 
  • Like
Reactions: Dartlec and pc1966
After I posted this I remembered that case of the crappy low IR cables, though in this case no real sing of moisture, etc. But it is quite possible they had the same batch of dodgy cable.

Otherwise it is hard to explain all circuits being rubbish without any obvious reason.

IR was fairly constant, much the same on 500V as 250V, and a slight increase in R with time if I held the tester energised.
 
It looks like a shipping container, basically a corrugated steel box but with two shuttered windows and a door (instead of the double end-doors that shipping containers use).
 
It looks like a shipping container, basically a corrugated steel box but with two shuttered windows and a door (instead of the double end-doors that shipping containers use).
Quite possibly the vibration of it being transported around has started to affect the insulation on the cables and we all know how well hire kit is looked after.
 
  • Like
Reactions: pc1966

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

pc1966

Esteemed
Arms
Supporter
Joined
Location
Dundee
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Enthusiast (Unqualified Hobbyist etc)

Thread Information

Title
IR low on site office
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
pc1966,
Last reply from
Strima,
Replies
5
Views
1,527

Advert