you are wrong !!

I fixed a problemm recently on a circuit without an earth and the "broken" cable was tripping the RCD

Back to the OP, wouldn't an urgent thorough inspection be required?? I certainly wouldn't touch this install without this first, and probably remedial workk before considering the CU.
 
I would say that the whole of the install would be worthy of a thorough inspection and test before any proposed works proceed as you will just end up inheriting the existing problems. If the MICC has not been correctly terminated then chances are that the magnesiun oxide within the cable could be damp as it is hygroscopic
i agree. by the way, it's hydroscopic
 
If the MICC has not been correctly terminated then chances are that the magnesiun oxide within the cable could be damp as it is hygroscopic


If MICC, this wouldn't cause the loss of earthing etc, but would cause far bigger problems to this installation!! lol!!
 
you are wrong !!


Lots of misleading information on this post.

IMO the above should explain why they think you need a CPC for the device to work !

I am with geoffsd on this !

So every class 2 bit of equipment that is used with RCD protection will not work !
 
By someone who knows what they're doing.
Sorry op mate but I don't think you've got the right stuff for this one.

Agreed! Old pyro can be a royal pain in the butt and that's with tools and experience.

OP should walk away from this one.
 
Agreed! Old pyro can be a royal pain in the butt and that's with tools and experience.

OP should walk away from this one.

Only when it was installed by muppets or has been interfered with by other muppets... lol!!
Otherwise it will outlast the original installer...
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
No earth... Zs and rcd
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
30

Advert

Thread statistics

Created
james king,
Last reply from
Engineer54,
Replies
30
Views
6,632

Advert