I'm running a supply to a garage sub-main via 10mm2 SWA from the supply head cupboard. There not enough space in there for a standard switchfuse, but I can get in a slim din rail enclose for a single 50A MCB.

This would mean the 25mm2 tails would have to go into top of MCB, with SWA gland at bottom. This reverses input through the MCB, but this shouldn't make any difference to its operation, this being AC.

I'm worried about the struggle with the fat live tail into the top of an MCB, so wondered if anyone had encountered this situation and come up with a better solution. Any good ideas gratefully received please!
 
Why not reduce the size of the supply cable from 25mm as the 50A mcb will limit the load.
 
agreed. use 10mm then you can feed in at the bottom and out the top.
 
So as you and Sintra suggest, just have short 10mm tails for rec isolator to my mcb enclosure? That would work - deceptively simple! I like it :-)

If the live supply goes in bottom then swa gland would be at the top - not pretty - haven't done that before. wouldn't it still be better to have swa exit bottom, then straight out through bottom of cabinet, than do a loop?
 
gland the SWA in at bottom then dress tails inside to top. vice versa with supply tails.
 
Well, it's in - but what a pig!

I'd bought a slim DIN rail enclosure to house the single MCB protecting the circuit. However, I had failed to notice until I got to site that this CED enclosure has a casing that splits front and back, with back part holding DIN rail, and front part having the depth for the SWA gland entry. So getting the wiring in there and getting it all mounted on the back board was a nightmare.

I ended up crimping the neutrals running alongside the MCB, but bringing the SWA earth and armour earth from gland nut both out to the MET.

The existing meter tails came straight from REC switch to consumer unit inside house, so I put a Henley block in there, and ran short section of 10mm T+E from there to new MCB. I left the T+E sheathed for protection, just adding the cpc at end away from Henley block to the MET also.

It's not pretty, but it's sound. Other end is RCD garage unit.
 
Well, it's in - but what a pig!

I'd bought a slim DIN rail enclosure to house the single MCB protecting the circuit. However, I had failed to notice until I got to site that this CED enclosure has a casing that splits front and back, with back part holding DIN rail, and front part having the depth for the SWA gland entry. So getting the wiring in there and getting it all mounted on the back board was a nightmare.

I ended up crimping the neutrals running alongside the MCB, but bringing the SWA earth and armour earth from gland nut both out to the MET.

The existing meter tails came straight from REC switch to consumer unit inside house, so I put a Henley block in there, and ran short section of 10mm T+E from there to new MCB. I left the T+E sheathed for protection, just adding the cpc at end away from Henley block to the MET also.

It's not pretty, but it's sound. Other end is RCD garage unit.

Sounds like it was your day to take one for the team! We've all been there.....
 