Discuss no supply on part of ring main in the UK Electrical Forum area at ElectriciansForums.net
B
BrainD
I have suddenly lost supply in all of the sockets in one of my bedrooms yet all of the other rooms on that ring main are OK. I've no idea what happened because it was only discovered when I tried to switch on a bedside lamp. Ceiling lights work OK. No main fuses were tripped and I've tried switching the mains supply switch off and on but no success.
Grateful for any help.
Sounds like a bad connection but to lose sockets on a ring final circuit you would need this to occur in two places. If you feel confident turn all power off and check the socket connections.
how many sockets are not working ?,what is the fuse or mcb (protective device)ratting you it may be a loose connection with both sockets spurred of the ring (spur off a spur)depending how old the wiring is as it was allowed once.
Apparently you disagree westward10 but I can't see how you can reconcile your view with the definition of a circuit given in BS7671 Part 2.
Thanks for all your help, problem solved.
Just for the record the property is only 14 years old and we have occupied since new so the wiring is probably bang up to date and there are no spurs on this circuit. The room has 6 no double sockets and all were down.
I made sure the bedside lights were in the ON position and systematically opened each socket and I found that the bedside lights flickered when I opened particular socket and by tightening the live connection the problem was solved.
Since this socket is behind a piece of furniture and has probably only been used on the odd occasion in 14 years, what I don't understand is how the connection has worked loose in the first place?
Thanks again for your help and I would be very interested to hear what you think may have caused the problem.
it's possible. once had one of the tails become a poor connection in a 1970's CU. was 2007 when the problem surfaced as a burnt terminal.
as for your fault. if the RFC is in fact an intact RFC, then a single loose connection would not cause the loss of any sockets apart from the one with the poor connection, as other sockets would still have a working supply from the other leg.
Most screw terminals will become loose over the years, this is caused through a number of factors, copper being a soft metal means it is more susceptible to expansion/contraction under load.
Alternating current (AC) by its very nature causes very small deflections in the copper.
Try for yourself with an off cut of copper cable, tighten it without squashing it (over tightened) leave for a day or so then return to it and you'll probably get an easy quarter of a turn on screw again.
Reply to no supply on part of ring main in the UK Electrical Forum area at ElectriciansForums.net
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Hi guys I am looking to add 4 additional sockets for a room that is being converted for a bed ridden person. The room at present has no sockets in...
Hope you're all well . I've had ring door bell 2nd generation hardwired for 1.5 yrs... it was connected to transformer which is connected to the...
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...