The Ghost
Could be loose connections upstream of consumer unit. Have you done a ramp test?
Discuss Nuisance tripping. in the UK Electrical Forum area at ElectriciansForums.net
think OP's remit was a CU change.Several things spring to mind:
That IR reading is far too low for new wire
Did you wire it or just test it
Do you know which circuit has the low reading
Why a big dual board in a new home
Have you ramp tested the rcds
Could you reconfigure the board for rcbo's
Do you have outside circuits
Etc etc
think OP's remit was a CU change.
I read post #3 where he mentioned "existing circuit"
This thread is a huge advert for RCBO boards
I don't understand why anybody fits dual boards any more
10 way split board, fully loaded £60
So it works out cheaper to buy RCBOs as a CU package and just put the CUs to one side.£110 will get you about 6 or 7 rcbos + board
10 way split board, fully loaded £60