B

buzz30

hi all, just after a bit of advice have had a oil boiler fitted in a outhouse the company also wired it up. They took a 3amp fused spur off the the immersion spur ran 1.5mm 4 core 14 meters to outside junction box 3 meters of armored cable to another junction box then 5 meters in the out house to the boiler. Does this seem ok or do I need to get a electrician in. Thanks
 
sent you a pm. i'd get it checked. sounds like a bodge to me.
 
Did you get any paper work from the company what showed they have tested the circuit, like a Minor Electrical Installation Works Certificate?
Have you paid up fully for the boiler?
Did they say why 4 core?
 
Waiting on the paperwork, the 4 core was because it needed a permanent live for a frost stat I think he mentioned it when quoting.
The other 2 companies that quoted advised the same junction box armored cable junction box but different cable sizes because the gap between the house and outhouse is about 3 meters had to go under the path.
 
My only concern is cable size and route, we had next door done 2 years ago which has identical boiler position but they run the cable in one complete length with no junction boxes armored cable I’m now wondering if that one is wrong and the new one is ok.
 
This is where pics can help folks to comment. Having said that, if it was able to be done in one run of cable there's less to go wrong over time.
 
I'm not sure why 4 core though.
It looks like the boiler needed a 3A supply which they took from the 3A spur. A 'permanent live for a frost stat' could be taken from the 3A spur that they have wired from, only needing 3 core.
If anyone is familiar with these boilers then maybe someone could correct me.

OP:
Are you using the switched fuse spur to switch on the boiler?
As above, a single cable would be better, but from what you describe, using junction boxes is not against regs... As long as it's been done correctly.
 
Would 1.5mm have been correct size?
I think the armored is because it runs under the flower boiler where the other house is all concrete.
 
that's where i've been going wrong. not been boiling the flowers.

upload_2018-12-12_10-20-16.jpeg
 
Would 1.5mm have been correct size?
I think the armored is because it runs under the flower boiler where the other house is all concrete.
Hi - let's say the load was 3A then voltage drop is
0.029 x 3 = 0.087V per metre (figures from Table 4D4A) . If I understand correctly you've about 20m run, so less than 2V drop in that length or less than 1% which is Ok.
 
Hi - let's say the load was 3A then voltage drop is
0.029 x 3 = 0.087V per metre (figures from Table 4D4A) . If I understand correctly you've about 20m run, so less than 2V drop in that length or less than 1% which is Ok.
too much information before beer o'clock. :D:D:D.
 
Would 1.5mm have been correct size?
I think the armored is because it runs under the flower boiler where the other house is all concrete.

1.5 is bigger than required, but it's the smallest size armoured cable is commonly made in.
 
I'm not sure why 4 core though.
It looks like the boiler needed a 3A supply which they took from the 3A spur. A 'permanent live for a frost stat' could be taken from the 3A spur that they have wired from, only needing 3 core.
If anyone is familiar with these boilers then maybe someone could correct me.
.

A basic oil boiler normally requires a switched live, neutral and earth, the frost stat requires a permanent live. Therefore four conductors are normally required to a boiler in an outbuilding.
From the OP's description the fused spur is located in the house rather than the outbuilding so it's not possible to connect the frost stat directly to it.
 