if you look at it this way if you have 20 x 60watt lamps all running at the same time that eguals 1200 watts which = 5.21 amps which is under the rating of the 6amp fuse at present apply diversity and its very unlikely the the little oldlady is going to light up her home like blackpool iluminations so i would go for a 6amp type c mcb which allows for ahigher start up current ect which should stop the tripping !
if you look at it this way if you have 20 x 60watt lamps all running at the same time that eguals 1200 watts which = 5.21 amps which is under the rating of the 6amp fuse at present apply diversity and its very unlikely the the little oldlady is going to light up her home like blackpool iluminations so i would go for a 6amp type c mcb which allows for ahigher start up current ect which should stop the tripping !