bonn1ett

Hi everyone,

I am fairly new in the trade and wondered if anyone can throw some advice my way. I recently went to a fairly old property as all the lights had gone off due to a lamp blowing in one of the light fittings which in turn blew the 5amp fuse wire in the board. Apparently this had happened a few times with the lamp blowing/popping out of its fitting?

There is one lighting circuit and hence one 5amp fuse for the whole house - upstairs and downstairs. I recommended to the customer (elderly lady) that the fuse board needs updating and that two circuits are needed for the lighting - upstairs & downstairs. The customer is happy to have a new consumer unit put in but does not want any re-wiring done - obviously if there is any faults found on the existing wiring then i will recommend strongly that the work be carried out.

My question is this, with regards to only having the one lighting circuit, could i perhaps use a 10amp breaker as opposed to a 6amp to cover the whole house - as long as the cable rating is higher than this (not sure if its 1mm or 1.5mm being used, need futher investigation).

any advice would be great
 
Its quite common for lamp to trip a mcb when it blows but not all the time . I would certainly have a good visual of the original installation before upgrading the board i know this subject has been covered many times but i personally do not go over board with testing ect before board changing because these new boards will still throw things up even after testing i just make the client aware there could be problems with extra cost ( be truefull ) then if there are remedials works just crack on mate
 
yeah will inform her that it may cost more if problems arise. Just want to do a good job and have it comply with the regs and keep the customer happy, just starting out so want to build a good reputation!

thanks for all the help.
 
and on what basis are you condemning this board?....You can get MCB upgrades for BS3036s....yes i understand about all the lighting being on only one way but that isn`t a basis for condemning this board.....as long as its in good condition and fit for continued service then its a 4......
 
  • Like
Reactions: 5 people
i agree with glennspark completely .. a little old lady i'd go for the mcb upgrades myself .and keep the costs down
exactly my point mate.....just condemning something because its not to the 17th edition......thats the idea with PIRs innit.....noticed no mention of a PIR from the o/p n all....talking about the lighting arrangements.....had a look at the wireing for those?...cpc present?...class 1s?......PIR first here mate.....
 
Last edited by a moderator:
  • Like
Reactions: 5 people
i'm gonna make a complaint thats the 3rd time i've agreed with you . is it some form of hypnosis over the web and ok i shall give you all my bank details master
 
  • Like
Reactions: 2 people
and on what basis are you condemning this board?....You can get MCB upgrades for BS3036s....yes i understand about all the lighting being on only one way but that isn`t a basis for condemning this board.....as long as its in good condition and fit for continued service then its a 4......

At long last the voice of common sense.

All to often we get threads along the lines of it’s not 17[SUP]th[/SUP] so it’s got to be ripped out.
 
  • Like
Reactions: 3 people
and on what basis are you condemning this board?....You can get MCB upgrades for BS3036s....yes i understand about all the lighting being on only one way but that isn`t a basis for condemning this board.....as long as its in good condition and fit for continued service then its a 4......


Only on the basis that the single circuit is occasionaly blowing when a lamp fails...which is hassle for the homeowner as a fuse has to be repaired.
Plug in MCB's are normally type B...which would offer no advantage other than an easy reset...a CU change would enable a type C which should reduce or prevent nuisance tripping.
I dont think anyone is condemning the 3036 CU..simply that there are better options.
 
  • Like
Reactions: 1 person
but its not a wrong option is it
i would always give the cheaper option as well and try and explain the good and bad in both options after all she is an old lady
 
  • Like
Reactions: 1 person
If anything...the old rewireables would be better (characteristic wise) than the B type....but as has been said already....its the convenience factor n all....
 
suggest that if the lighting is all 1 circuit, dis the feed between downstairs and upstairs lights and feed a new T/E to the upstairs
 
  • Like
Reactions: 1 person
My lights are all on one circuit (1970s build house) and can't see the point of splitting them. All the hassle of boards up, making good, etc. I can't remember the lighting MCB ever tripping (or the 3036 fuse before it for that matter) in 15+ years. That's mixture of part tungsten and part CFL lamps used.
Daz
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Old re-wireable fuse board change
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
37
Unsolved
--

Advert

Thread statistics

Created
bonn1ett,
Last reply from
DPG,
Replies
37
Views
4,050

Advert