It may be worth the customer enquiring of the DNO the cost of providing a separate supply to the garage. Depending on routing on their side, this may be relatively inexpensive and would give greater scope.
 
thanks everyone.
the garage/shed will be around 9mtrs x 10 mtrs.
their will most likely be water but no gas.
i will look into the possibility of getting a separate supply in
 
As you haven't provided a design current it is easier to use In. This also means you are covered for volt drop right up to the point of overload of the distribution circuit. 32A you could go 10mm, if you go 16mm, you can do 50A. Using In instead of Ib and youve got a VD just under 5% for both.

Check Ze. You have TNS so could be up to 0.8 ohms already....

C40 60890 max Zs is 0.54

R1+R2 for the 10mm is 0.35

R1+R2 for the 16mm is 0.23
 