To supply power to new garage 20 meters at bottom of garden from main house.

Plan to run a three core 4mm SWA to garage, fit a metal clad two way dB with 30ma RCD in garage. Using one off the three cores together with the armour as cpc.

At the house end terminate swa in An adaptable box adjacent to house BD and use 6mm twin and earth to connect lives and earth to a 20A spare way of existing plastic board.
This incorporate an RCD covering whole installation. There is an earth rod so I assume this is a TT installation.

Assuming Zs at garage is ok. This is what I planed

However lots of talk about fitting an earth rod at garage end.
In your opinion should I also fit an earth rod at garage end and common back up earth. Also I think I could ask for supply co for a pms at this site there is a new cut out or would this be just complicating things
 
This old IET pdf should help it is a little dated, in 2005 we did not have RCD protection like we use today, but general principle is the same.

The problem is Part P, the fees charged by the local authority are silly, in rest of UK using a 13A supply from a FCU could get you around Part P but since your in Wales no real way around it.

The other problem is volt drop, corrected and within lighting requirements should be able to use around 34 meters of 4 mm so should be no problem.
 
Duplicate thread see following link.
 

Reply to Outbuilding or garage supply in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
414
Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
697
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
I have a strip light in the kitchen operated from a single switch. I want to replace it with a straight bar 4 spot array. There are three supply...
Replies
2
Views
435

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock