thanks for your reply's it was a circuit problem but i've solved it i hope. I ran the outside lights off a fused switched spur and that solved it. The circuit kept tripping when i dropped a switched live down to a switch from the light.
Hi,
Hi
Why was it tripping in the first instance,thats the question:confused:
Re: Outside shed problems
Need a bit of advice on this one,
I need to supply a 4 way consumer unit in a block shed from the main consumer unit in the house.
The supply from the four way db will be powering 10 double sockets, 2 lights and 3 outside lights.
What size SWA would I need to use and if I install a ring in the block shed would it be ok to use a 32 amp breaker as the supply to the shed will be running on a 20 amp breaker iin the house?
First thing I would say is that if you are installing ten double sockets there must be a reason in which case a twenty amp supply is not likely to be adequate.
As for a 32amp breaker downstream of a 20 amp, this will not give you any discrimination and the 20amp will trip at the source before the local 32amp in the building.
If the building is outside the equipotential zone, which it sounds like it is, you will also need RCD protection.
My advice is to establish the maximum load, ensure a suitable supply is available and then work out what parts and cable you need.
Take it steady:confused:
Reply to Outside lighting problems in the Canada area at ElectriciansForums.net
Hi, Heavy industrial spark here, never do house bashing hence the question. I currently have a light switch at the front door not doing anything...
Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Hi, I have run some outside lighting for a customer in Hi-tuff cable. He now wants 2 additional lights run across scaffolding which has been put...
Hi there, I have an outside light that is turned on with a switch from inside and would like to change it to a PIR version incorporating an...
Hi All, I own a country Villa out in the Spain countryside. Was having problems with water pressure so local tradesmen advised to get a water...