Discuss Outside sheds TT or not TT in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
sevuk
This is a topic we discussed while doing 2391. It's not something I've really thought of or need to for that matter.
If a shed far down the garden has its own CCU, should it be fed with a two core armoured glanded into a plastic box and have its own electrode?
The theory being especially if it is a metal clad shed, isn't there a risk of electric shock if the shed is brought up to the same potential as the house if there is a fault in the house?
Small loads like lights would more than likely be fed from a circuit in the house and if rcd protection is provided this should be adequate, but a workshop should be in its own faraday cage should it not? Or at least have an earthing conductor the same size as the bonding conductor in the house.
What do you guys do?
  • Garage-Shed Supplies.pdf
Arrgh what the hell....depends if the DNO has a particular dislike on the practise of exporting or extending (whatever) their PME supply or if there's anything extraneous, that make a TT more cost effective.
When would exporting a pme supply be allowed?
I can't see that being correct, but I've never been involved in it.
Without even thinking about it, I've often run in an earth cable with an armoured as part of the design, I've never tapped off a neutral.
Done a few times to detached garage for example, DNO had no preference, and TNC-S is mostly better than brilliant TT. The likes at the IET don't think so mind!
Come the 18th we will be putting in a rod on tncs ....... The regs writers just don't have as clue what they are suggesting ...
So export the earth and add as rod. ....
TBH honest I did a freebie job for old lady who lives next door, I thought about all scenarios, exporting a 16mm earth, tt'ing etc and went with what Murdoch suggested, PME and bang in a rod for good measure......
Freebie, how much did the rod cost ya ?
Reply to Outside sheds TT or not TT in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Hi all, I'm planning on adding some lighting to an old stone shed, there's currently a 2.5mm² SWA supply to the shed only supplying one IP rated...
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
5K
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Looking for some cabling advice for my garden project. I’ve put together this diagram below, which hopefully explains what I’m trying to achieve...