Customer is having 2 ovens, both rated at 3K55W each so 15.5A

Would the best way be to run two 2.5 radials on a 20A mcb or have them on a 4mm ring 32A breaker (or rad even to seperate them?)

Also, they are having an induction hob rated at 7K09W, 31A. Would sticking this on a 32A mcb be cutting it a bit fine? otherwise it's 10mm instead of 6mm.
 
With the 2 ovens there is no reason not to put them on the same appropriately sized radial as long as they are both within 2 metres of the control switch.

With the induction hob i would consult the manufacturer just in case there is a power factor associated with it.
 
So it would be ok to have them both off the same control switch? Didnt think you could do that?
 
So it would be ok to have them both off the same control switch? Didnt think you could do that?

It's ok, have a look at the On Site Guide Appendix 8.4
"A circuit of rating exceeding 15A but not exceeding 50A may supply 2 or more cooking appliances..." goes on to say they must be in same room and within 2metres of the switch.:)
 
I'm going to run two seperate rad's so in the event of a fault only 1 will trip. beafy ovens for a house, and to have 2! lol
 