I have traced both cables from start to finish and there are no joints in them and the outer sheath looks in good condition. Still not sure what code to give it
 
With a difference of 0.05 ohms, the extra length cant be that much. I mean the difference could be down to slight movent of the croc clips when testing. Look in the OSG and do a few calcs and you will see how long each cable is. When you measure end to end on a ring, the L N results can be within 0.05 ohms and still be ok. At worst, going by what you have described, I would say C3 but as others have said its your call. Some wouldnt even code it. I may not code it if I was acctually on site looking at the whole picture.

Jay
 
You can work out the load sharing of the conductors, but a simple clamp meter test should suffice. Assess the load and the supplying PD and make an engineering judgement based on your findings.
 