rll13

Hi,

I would like an opinion regarding Park Homes/ Static caravans. At present each dwelling is fed via buried 2.5mm 3 core SWA with 20amp C mcb from a local distribution centre. The armour and one core are connected together to provide a combined earth.

My question is that measured Ze at the Park home connection is around 7 ohms. The home has a 30ma RCD as an incomer. As this is a TN system and not TT would anyone adivise an additional earth stake to try and lower the Ze or will this introduce additional problems.

If this were a TT system the readings comply with regs. The RCD trips at rated values.

Many thanks

RL
 
Hi RL.

There is a section in the regs that covers this type of install.

However, i think you could either leave the existing earthing alone and TT at the supply end, or you could TT each pitch.
 
Hi Jason

Thanks for the input. These homes/caravans are not the touring type and I think are considered to be houses in there own right. I can't find any definitive section in the regs regarding them. Regarding the Ze from the combined core/armour (TN) and considering it is lower than a stake and the input to the caravan is an RCD, would you consider this to be sufficient to satisfy regs.

RL
 
This value is probably lower than a stake, however, it is too high for a TNS system (0.8).

Therefore, i would definatley stake each 'pitch'.
 
Hey there.

Pesonally I would look at converting each pitch into TT installation and treating it almost as a caravan type pitch.

The distribution points would be on a TN-S system providing the Ze readings at these points are within limits, with all supplies to statics then being TT.

As J said your values of Ze for a TN system are way off and so don't comply.

Hope this helps:D
 
Good advice guys, many thanks. I think it make sense to make everything TT.

Regards

RL
 

Reply to Park Homes in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock