Discuss Park Homes in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
R
rll13
Hi,
I would like an opinion regarding Park Homes/ Static caravans. At present each dwelling is fed via buried 2.5mm 3 core SWA with 20amp C mcb from a local distribution centre. The armour and one core are connected together to provide a combined earth.
My question is that measured Ze at the Park home connection is around 7 ohms. The home has a 30ma RCD as an incomer. As this is a TN system and not TT would anyone adivise an additional earth stake to try and lower the Ze or will this introduce additional problems.
If this were a TT system the readings comply with regs. The RCD trips at rated values.
Many thanks
RL
Hi RL.
There is a section in the regs that covers this type of install.
However, i think you could either leave the existing earthing alone and TT at the supply end, or you could TT each pitch.
Hi Jason
Thanks for the input. These homes/caravans are not the touring type and I think are considered to be houses in there own right. I can't find any definitive section in the regs regarding them. Regarding the Ze from the combined core/armour (TN) and considering it is lower than a stake and the input to the caravan is an RCD, would you consider this to be sufficient to satisfy regs.
RL
This value is probably lower than a stake, however, it is too high for a TNS system (0.8).
Therefore, i would definatley stake each 'pitch'.
Hey there.
Pesonally I would look at converting each pitch into TT installation and treating it almost as a caravan type pitch.
The distribution points would be on a TN-S system providing the Ze readings at these points are within limits, with all supplies to statics then being TT.
As J said your values of Ze for a TN system are way off and so don't comply.
Hope this helps:D
Reply to Park Homes in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Hay guys and gals, doing my first park home CU change. I cannot find a copy of an installation cert for a portable dwelling can anyone point me in...
Am I over thinking this, Pitch socket for caravan TT system 16 amp MCB, Rcd protection 30ma, supply 2.5 flex to DB in caravan also RCD...
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Afternoon all, Got a bit of a strange one (by my usual standards anyway). Job is a large barn conversion, done years ago, there's loads of work to...