As others have said - whilst it's potentially causing a problem for the future, there's nothing 'wrong' with it today. And you have to ask yourself what the alternative is if you have different circuits in a chased wall scenario with accessories below/alongside - you've only got three choices as anyone who's ever read 'We're going on a Bear Hunt' will agree - around it, over it or through it!
 
One of the biggest problems with this industry.

Too many try and pass off personal opinion/preference as a regulation.

Hence I now always ask what the regulation is that is being breached.
Whilst that may be true it is worth remembering 7671 is non-statutory and seen as a minimum standard. If you want to go over and above that you can.

Nothing wrong with a C3 and 134.1.1 - You could FI but this would fail the install and be deemed excessive. A C3 at least puts attention on it, even if thr client does nothing with it.
 
Whilst that may be true it is worth remembering 7671 is non-statutory and seen as a minimum standard. If you want to go over and above that you can.

Nothing wrong with a C3 and 134.1.1 - You could FI but this would fail the install and be deemed excessive. A C3 at least puts attention on it, even if thr client does nothing with it.
That's a whole new can of worms but just a little context.

In this particular situation I returned to the job to find the fire alarm FP200 and the intruder alarm cables routed through my containment.

I could have been a real stickler (not the word I'd normally use 😀) and insist the whole lot was removed, or removed it myself.

Certainly there are black-and-white reasons why the intruder alarm cables could not be in there, its not open to conjecture, so these were pulled out and rerouted.

The amount of work involved in rerouting the FP200 was substantial, none of the cables would have been long enough. So, out of the kindness of my heart, I allowed them to remain.

If you're going pull apart other peoples work that is not in contravention of the BBB, and incur additional costs, you'd better have a better reason than "I don't like it, 134.1.1 poor workmanship" these things have a habit of escalating quickly.
 
That's a whole new can of worms but just a little context.

In this particular situation I returned to the job to find the fire alarm FP200 and the intruder alarm cables routed through my containment.

I could have been a real stickler (not the word I'd normally use 😀) and insist the whole lot was removed, or removed it myself.

Certainly there are black-and-white reasons why the intruder alarm cables could not be in there, its not open to conjecture, so these were pulled out and rerouted.

The amount of work involved in rerouting the FP200 was substantial, none of the cables would have been long enough. So, out of the kindness of my heart, I allowed them to remain.

If you're going pull apart other peoples work that is not in contravention of the BBB, and incur additional costs, you'd better have a better reason than "I don't like it, 134.1.1 poor workmanship" these things have a habit of escalating quickly.
That can be true and yes you would hope you have more than 134.1.1 but its still an option, depends how how much it matters to either party as to whether or not to go down the route.

If the cables weren't weren't FP or appropriately rated then you've got more regs to add and probably clauses from 5839 and if you REALLY want to push it then I'm sure they would be something in the FS(RR)O 2005.

Anyway back to the thread 🤪
 
Whats not required?

A warning notice about voltages...

514.10.1 "Every item of equipment or enclosure within which a nominal voltage exceeding 230 volts to earth exists and where the presence of such voltage would not normally be expected, shall be so arranged that before access is gained to a live part, a warning of the maximum voltage to earth present is clearly visible".

Unless I'm much mistaken, that's the only regulation about voltage warnings. So for a standard low voltage three phase supply you don't need one. Yes there is 400v phase to phase but to earth it's only 230v so a notice isn't required. But as has been pointed out already in this thread, the regs are a starting point. There's nothing stopping you putting a 400v warning sticker on things, it's just not required.
 