orac77

Hi,This might sound like a stupid request but how with a standard pat tester do you test a cooker when you can not plug the 6mm into the s/o of pat tester or do you just croc clips on to cable then test.Thx
 
Thx for that,is that a FAT test then, its just that i was working at a house and they are going to rent it out and asked for the cooker to be tested.
 
Thx for that,is that a FAT test then, its just that i was working at a house and they are going to rent it out and asked for the cooker to be tested.
I just pat tested a cooker, it was a flex with plug for the ignitor but did'nt actually test the whole cooker
 
you can IR test ther cooker with a MFT or megger 500v tester. you also need to check continuity of cpcd tothe metalwork of the appliance.that's about it
 
This is all covered in the IEE Code of practice for the in-service inspecting and testing of electrical equipment.

Obviously a fixed appliance is not subjected to the tougher conditions of use as say a vacuum cleaner. Therefore testing intervals can be far more generous.
 
Its not a portable appliance , but when carrying out the fixed wire test it worth testing it in the same manner ( continuity , IR , Earth test ), especially if there is age to the cooker
 
Its not a portable appliance , but when carrying out the fixed wire test it worth testing it in the same manner ( continuity , IR , Earth test ), especially if there is age to the cooker

On that argument, you would do the portable appliances too!

These are separate tests unless the client has asked for them.
 
A cooker should still be tested. The idea that it's called portable appliance testing and a cooker is not intended to be moved during use is just a lazy play on words; swapping a plugtop for a FCU doesn't negate the need for testing.
 
Pat (Portable Appliance Testing), is in-service inspecting and testing of electrical equipment and not just portable appliances.
It should have really been called “APPLIANCE TESTING”
And as IQ Electrical said it is covered in the
IEE Code of practice for the in-service inspecting and testing of electrical equipment.
Every pAT tester should really have a copy of it as this is what you are supposed to be working to.

It does NOT just cover portable appliances Nor just appliances with a plug on

IEE Code of practice for the in-service inspecting and testing of electrical equipment.
Refers:

Page 2 fig 1.
The code of practice provides guidance on the inspection and testing of portable, movable and hand tools and equipment connected by means of a cable or cord connected to a outlet plate; appliances to build in; IT equipment; extension leads, multiway adapters and suppressor adapters.

Extract from Section 15.2 Page 72.
Equipment that is permanently connected to a flex outlet type of accessory can more easily be tested using an insulation/continuity test instrument with the test leads connected directly to the accessory terminals. The supply to the accessory is required to be isolated and proved dead at the point of work before testing commences.

-------------------------------------------------------------------
you could make up your own test lead to pat tester to do this
this is something i did with my pat tester so i could do the earth bond test at 25Amp as most continuity testers only do the earth screen continuity test @ approx 200mA
 
Last edited by a moderator:
-------------------------------------------------------------------
you could make up your own test lead to pat tester to do this
this is something i did with my pat tester so i could do the earth bond test at 25Amp as most continuity testers only do the earth screen continuity test @ approx 200mA

So how did you do this ?
 
It is all explained in the IEE Code of practice for the in-service inspecting and testing of electrical equipment. I would carry out a continuity and nsulaltion test also a formal visual check
 
you could make up your own test lead to pat tester to do this
this is something i did with my pat tester so i could do the earth bond test at 25Amp as most continuity testers only do the earth screen continuity test @ approx 200mA

So how did you do this ?

I used a 2 metre uk plug to IEC lead, cut the IEC off and fitted alligator clips to the earth. live and neutral.

I also have another lead same but without alligator clips (just bear wire) which i use if a cant get alligator clips on, that I screw into same terminals the cooker is in.
simples.

Note: as mentioned in my previous post you MUST make sure the cooker is isolated and proved before doing any of the above.

Also using these leads if you pat tester has this function it is possible to do Earth Leakage tests on most domestic cookers. NB you will need to disconnect the input earth lead from the outlet plate to do this test (make sure you re-connect it when you have finished pat testing).
Note this is a live test Powered from your pat tester and most pat testers can only supply up to a max of 13Amp (2990w).
so don't try testing the whole cooker at once.
you really need to be sure (ideally have manufactures spec) of the individual rings, ovens & grill and if any are above the rating of your pat tester DON'T do this test on that item.
the beauty of this test is if you have got a problem with earth leakage in the cooker it gives you an idea were the problem is.
 
Last edited by a moderator:
Thanks for that - trouble is invariably you're at a client that says "Oooh Noo! We don't want the power off - that'll upset all sorts of stuff."

So an "In Situ" test is the best you can provide - at least 100mA earth bond test is better than not at all, and visuals of course (in this case) are the main criteria for this equipment. (Seaward recommend from their COP Rev3 seminars.)
 
Thanks for that - trouble is invariably you're at a client that says "Oooh Noo! We don't want the power off - that'll upset all sorts of stuff."

So an "In Situ" test is the best you can provide - at least 100mA earth bond test is better than not at all, and visuals of course (in this case) are the main criteria for this equipment. (Seaward recommend from their COP Rev3 seminars.)

You only remove power from the Cooker Circuit not the whole premises

The way I'm doing it insitu is still using my pat tester to bond test at 25Amp, insulation test and Load/earth leakage tests.
you can disconnect the cooker if you want and connect cooker lead via a quick cable connector to your pat tester think they are called keynector or something like that.

but I don't see the need to disconnect it when can you do all the tests insitu, even the IEE Code of practice for the in-service inspecting and testing of electrical equipment mentions doing it insitu
 
Last edited by a moderator:

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Pat test on cooker
Prefix
N/A
Forum
Electrical Testing & PAT Testing Forum
Start date
Last reply date
Replies
18

Advert

Thread statistics

Created
orac77,
Last reply from
ian.settle1,
Replies
18
Views
32,455

Advert

Back
Top