Just to hi-light here the Flash test 1.5kv for Class I and 3Kv for class II is what is required as a test by the manufacturer, most PA-Testers won't need to do it, if an item is been serviced though or having repaired done (i don't mean a new plug or flex) its should be subject to the appropriate flash test for its class.... the flash test on class II should be tested to all points exposed whether insulation or conductive, the flash test on class I needs to be to insulated parts only for obvious reasons.
If you are not in a similar industry to me then you may not ever use a flash test but having 3Kv handy at the end of a probe is sometimes fun for feeling like a mini-THOR!
http://www.testing-and-installation.co.uk/3a_guide_to_pat_testing.pdf
If the OP reads the link he can access whether the accused is falling short of his job.