Carried out a ccu replacement and then started testing, my PFC was 38A & 6.11 ohms. Just wanted to have some thoughts as mine was that there must be a poor connection or break in the main cpc?

Thanks
 

Attachments

  • D1E90D36-5177-4A0A-82A1-0AA60AF32164.jpeg
    1.4 MB · Views: 36
Did you do any testing before swapping the CU?
 
Carried out a ccu replacement and then started testing, my PFC was 38A & 6.11 ohms. Just wanted to have some thoughts as mine was that there must be a poor connection or break in the main cpc?

Thanks
Presumably that was the Prospective Earth Fault Current (PEFC) as opposed to the Prospective Fault Current (PFC). The Prospective Short Circuit Current (PSCC) must have been substantially greater otherwise the volt drop on the loads would have been enormous to the point where things just wouldn't have functioned.

PFC is the greater of the PEFC and the PSCC.

If it was a TN-S supply then an emergency call to the DNO would be in order assuming that the Earthing Conductor is correctly connected at the MET.
 
No i don’t, and no previous records available
It is advisable to test before carrying out any work to identify any issues and ensure the installation is fit and safe for continued service.

You need to check the main earthing conductor terminations, if at the DNO end you will need to call them out to rectify. What sort of installation is it?
 
Carried out a ccu replacement and then started testing, my PFC was 38A & 6.11 ohms. Just wanted to have some thoughts as mine was that there must be a poor connection or break in the main cpc?

Thanks

Anytime I've had readings like that it has always been down to an external fault on the DNO's side. As Strima mentioed, it is always wise to do your testing before a board change rather than afterwards!
 

Reply to PFC reading in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K
Hi all, I have a question regarding the breaking capacity of circuit protective devices. So, the breaking capacity rating of devices in domestic...
Replies
13
Views
3K
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
564
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
622

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock