Hi I'm currently coming to the end of my apprenticeship having completed my city of guilds level 3 and 17th.
i completed my am2 last week and passed everything apart from my testing and inspecting. I would just like abit of advice on how to complete the pfc test correctly as I failed on that and also, when Doing the insulation resistance test, i completed it globally but never done the lighting circuit as it has 2 way and intermediate switching. When IRing that circuit do I go between L-E L-N N-E and switch each switch as I do so?
any help would be appreciated as I have my resit on Thursday
thanks
 
Hi dude,your IR testing should be carried out,if possible,between ALL conductors,and to enable this,on a lighting circuit with strappers/intermediates,you will need to ensure that these conductors are included,by operating the switches accordingly.

Your PFC on a 3 phase installation,will,depending on your test instrument,have to make allowance for the fact that an increase in the magnitude of any fault current exists between phases,in relation to one between a phase and neutral.

The accepted rule of thumb,is that this will generally be twice the value. The calculated value is slightly less than this,but this errs on the side of safety...as the book says...talking of books,you need a GN3...it's packed full of this carry-on...and is much more cheery than the TV news at the moment :winkiss:
 
One method for calculating PFC, is to measure between each phase and neutral, then adding the two highest values together.
 
Hi I'm currently coming to the end of my apprenticeship having completed my city of guilds level 3 and 17th.
i completed my am2 last week and passed everything apart from my testing and inspecting. I would just like abit of advice on how to complete the pfc test correctly as I failed on that and also, when Doing the insulation resistance test, i completed it globally but never done the lighting circuit as it has 2 way and intermediate switching. When IRing that circuit do I go between L-E L-N N-E and switch each switch as I do so?
any help would be appreciated as I have my resit on Thursday
thanks

https://www.youtube.com/watch?v=KOyLsi1GFqg have a look at this
 
PFC:
Generally do not test the PFC between phases as some meters cannot safely measure this, calculation as twice the single phase fault current is permitted.
At the origin (as this is the highest fault current)
Test L1 to N, L2 to N, L3 to N, multiply the highest value measured (they should all be similar) by 2, record this as PSCC.
Test L1 to E, L2 to E, L3 to E record the highest value measured as PEFC.
The PSCC recorded will be the highest value and this is the PFC that is compared to the breaking capabilities of the protective devices.

IR with two way switching:
all loads removed sensitive devices linked out.
Test L to N, L to E, N to E (if 3 phase then each line to each other line and to earth and to neutral, ten tests)
Switch the first switch and test the L to N and L to E again (no need to test N to E as this has not changed with a single pole switch)
Switch the second switch and test the L to N and L to E again.
record the highest values appropriately.

If you have more switches then sequentially switch each switch and measure again each time, this is a bit of overkill as you can see from the below diagram of intermediate switching that if the lights would be on then you test all conductors, but doing it this way means you have covered all options.
The situation is similar for two way switching, there are multiple paths to cover with the IR testing.
3 wire crossover.jpg
 
As ever,Richard,very concise...i missed the note re;N/E single pole switches...so i will be self-harming myself with a short length of spiky VIR...:bow:
 
All I was doing was trying to look good by fluffing out your explanation and adding a picture; success, yeah!:wink_smile:
Glad you are taking your electricians penance seriously!:53:
 