I want to replace the pneumatic light switches in my communal hallway with PIR switches. There are currently four pneumatic switches operating over three floors. Is this a straightforward job, and what are the right PIR fittings to use?

thanks.
 
Not familiar with the term pneumatic switch mate but It's a straightforward job for a qualified spark.
 
you may not be able to fit PIRs art the switch positions as there may not be a neutral at the switch. ceiling mount PIRs are the most commonly used for your purpose, but that would entail floors up and some rejigging of the wiring.
 
i think we call it a LANDLORDS SWITCH you know push it in and a bit later it pops out . to be honest this is a job for an electrician i woild say a bit to much for the diyer
 
I operate a number of flats with different methods of switching. Using PIRs has caused light fittings to burn out. In one case we had to replace all the light fittings as the 2D bulbs were burning out after about 4 weeks. The problem seems to be a pulse from the PIR which upsets the light fittings. Even after fitting a capacitor it did not work. The quality of the fittings may have some bearing on the issue.
I am looking at replacing the pneumatic switches with electrinic timers but am not sure if this can be done.
The most reliable system I have is a switch ( MK make such a switch) in the fuse box controlled by wall switches. In five years we have not had any faults or lost a bulb!
 
2D fittings need to be switch on for a minimum of 20 minutes if you dont want to do this use PL lamps instead of 2D
 
why not use fittings with built in sensors stinel do a 2 X 18 PL and E matic due a 60w with microwave sensor
 
if you had few windows you could put in day/night sensor.. but a million bucks theres no windows and is why u asking
 