Well I was thinking twin and earth (e.g. 6mm) would be cheaper and easier to run under floor boards etc.Skip the twin and earth in conduit and run swa straight to board. What is the purpose of the t+e? Looks like part of that board isn’t rcd protected, get an mcb to fit it

So I could join the SWA into a IP65 rated box and attach a banjo, nut and cpc to Earth the SWA?The right hand side of your board with the lighting MCBs isn't RCD protected and the blank will be a spare way- so subject to a decent Ze you could simply fit an additional matching MCB for the new SWA, but it will have to be glanded properly, possibly into a small metal enclosure to ensure the armour is earthed. EDIT= Ah I've just seen your post stating T&E for the first part of the run, so the SWA can be glanded into a weatherproof enclosure with an earthing nut and lead to the CPCs.
Yes that's right. Have a look at earthing or 'Piranha' nuts though, easier and IMO better than the old Banjo method. I'd be using 3 core SWA though.So I could join the SWA into a IP65 rated box and attach a banjo, nut and cpc to Earth the SWA?
Afraid idk the ZE at present.Do we know what Ze is ?
Do we know if there is any extraneous ?
You don't want to put the garage on the RCD side, just asking for trouble for the rest of the house being tripped by garage trouble.Cheers for the replies, much appreciated.
So the db is in the porch on the ground floor (highlighted red) and the first floor pic with red lines is my proposed route going under the floor boards or up into the loft.
You mentioned SWA all the way, is this because a join in cable with (T&E) would affect Zs readings or something?You don't want to put the garage on the RCD side, just asking for trouble for the rest of the house being tripped by garage trouble.
If it can go on the MCB side (assuming SWA all the way, end of cable Zs acceptable, etc) then do that.
Off hand I don't know if RCBO are available for that board should you need 30mA additional protection there, but keeping it off the existing RCD would be sensible.
However, you might want to plan to replace that CU in the near future anyway so keep enough cable slack to along that.
The point is that depending on the run, T&E might need RCD protection for Impact Protection. SWA definitely wouldn't for that reason. That is one reason why a few people are suggesting SWA all the way.ou mentioned SWA all the way, is this because a join in cable with (T&E) would affect Zs readings or something?
No joints and the t+e may need rcd protection depending on the route. Swa back to the board it a better solution and will cost minimally more due to the short length of the cableYou mentioned SWA all the way, is this because a join in cable with (T&E) would affect Zs readings or something?
Tbf I am leaning towards a board change at this point I won't lie.