Ok so lots to think about haha.

Realistically I'm leaning towards fitting a new board at the house with RCBOs. Then to supply the garage DB, a 40A MCB. Am I right in thinking I'd need RCD protection for this sole MCB?
No not as long as the criteria is met for disconnection /cable sizing /bonding etc

You need to know the type of earthing you have and if the garage door is actually extraneous or there is a likelihood of having anything extraneous that may require bonding.
 
No not as long as the criteria is met for disconnection /cable sizing /bonding etc

You need to know the type of earthing you have and if the garage door is actually extraneous or there is a likelihood of having anything extraneous that may require bonding.
I think I'll get some pics later with the board cover off for you all to have a look at to build the picture further.

I can't think that there is anything that will need bonding in the garage tbh, unless you count the metal board itself?
 
So far, all the advice offered has been on the technical side of things.
Has anyone pointed out that a new circuit, and/or a new consumer unit has to notified to local authority building control before work commences? (Or that the work be carried out by a registered competent installer.)
 
The right hand side of your board with the lighting MCBs isn't RCD protected and the blank will be a spare way- so subject to a decent Ze you could simply fit an additional matching MCB for the new SWA, but it will have to be glanded properly, possibly into a small metal enclosure to ensure the armour is earthed. EDIT= Ah I've just seen your post stating T&E for the first part of the run, so the SWA can be glanded into a weatherproof enclosure with an earthing nut and lead to the CPCs.
If you need this much guidance I'm not sure you should be taking the work on
 
Ok so lots to think about haha.

Realistically I'm leaning towards fitting a new board at the house with RCBOs. Then to supply the garage DB, a 40A MCB. Am I right in thinking I'd need RCD protection for this sole MCB?
If you’re using twin and earth depending on your route maybe, then no rcd in garage. If swa straight to board no rcd protection in house just in garage board. In all honesty this is really basic stuff that you should know.
 

Reply to Planning garage sub-main project in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
903
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
748
Hi all, Great to of found this forum. Much respect for keeping everyone safe! My background is in commercial data and Audio Visual. Been...
Replies
0
Views
562
Hello all. 17th edition sparky here, but not been on site for the last 3/4 years (had a bit of an accident). Just bought a house with a 16mm 3...
Replies
15
Views
3K
This is a question with probably so many answers and solutions, but I wondered how people would do it. I have a clients house which already has...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock