Hi,

I have a job to re-visit, a tripping MCB that protects kitchen lights and garden pond pumps.!!! Hmmmmm
Anyway, it's a 10A breaker and I have checked every junction box along the way of the SWA that runs for bloody miles in the garden. Everything seems OK, I have fixed the lights outside that were tripping this breaker also. Now it's just the 2 pumps for the pond. They last about an hour then trip the breaker.
It seems a very long run of SWA, maybe this is a factor, or maybe the breaker isn't larg enough. I don't know the rating of the pumps. The kitchen light total watts isn't high though.....
Some thoughts anybody?
Cheers

Nick
 
If the breaker was not large enough I would have thought it would trip on start up not an hour later. Sounds to me like one of the pumps is breaking down can you isolate each pump to see which one is causing the actual problem.


Chris
 
Pump needs stripping down and cleaning, just sorted some pond pumps for a mate of mine they were full of crud causing them to jam as they warm up as the water is not running through them properly to cool them
 
If its a hozelock titan pump, its probably full of water, they always leak. before diving in, use a multimeter to test the PD between the pond water and a good ground earth. Should be zero, but its not uncommon for pumps that are going to put a charge into the water, which of course is normally fibreglass or rubber insulated so nothing happens until somebody sticks a mitt into it and provides an earth

Any UV lamps, they can corrode and overheat and do funny things

Hope they have an RCB on that circuit?

Also a good practice to hang a Stainless steel rod into the water and bond it to earth so that the pond water is always safe (dont use copper or aluminium as they are poisonous to fish), although water isnt a good conductor, there is normally enough gunk, algea etc for it to conduct a little
 
had one similar..

UV lamp had corroded, MCB tripped when lamp plus pump turned on.. but not when operated separately..
swopped out the lamp and all was well.
 
This happens when no lamps are on. I have even isolated the pumps nearby with their 20A DP switch and the MCB still trips after a time.
I think the switch is knackered though, but even still I bypassed the switch so circuit straight to pumps and MCB still tripped.
All that's left for me to try is to disconnect each pump and see if one is faulty. They run for a while and have been cleaned out and so didn't really think it was the pumps.
I'm gonna change 20A DP switch at distribution board outside near pumps, change MCB at CU as it may be faulty and finally disconnect each pump in turn and see what gives??????

Cheers Everyone
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Pond pump Tripping MCB
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
8
Unsolved
--

Advert

Thread statistics

Created
ngoodson1969,
Last reply from
GT1,
Replies
8
Views
18,088

Advert

Back
Top