coatesykid

TNS earthing arrangement. tested ZE 0.18 ohms tested ring final circuit R1+R2 = 0.35 ohms so that makes the calculated ZS for the ring 0.53 ohms, but when I test the zs with my 1 month old fluke multi the reading comes out at 7.4 ohms can anyone tell me why this is the case
 
how did you get your R1R2?
what are your continuity reading's for P-P, and E-E?
 
Last edited by a moderator:
Have you reconnected your main earth after checking your Ze (maybe all you're seeing is any parallel paths when Zs testing your circuit).
 
Last edited:
got my r1 r2 by cross linking in cu and testing at sockets, P-P 0.3 ohms E-E 0.4 ohms aprox yes reconnect main earth
 
Last edited by a moderator:
also first time i tested it was the same and they was a fault on the circuit so I re-wired the whole ring and put new socket fronts on
 
all sockets do u think the tester could be faulty

no because you got a low Ze reading. Trusting that you reconnected the earth at the DB, it sounds like further investigation is required. I would test your meter on another circuit, like cooker, and a lighting circuit, and see what readings you are getting there. Better still test in your home.
 
how could reading be high on just 1 socket when all the sockets was less than 0.4 ohms r1 r2 test and the main earth is 0.18 ohms wouldn't that mean no mater the socket tested the zs reading should be no more than 1 ohm
 
one socket could have been spured off, with a loose connection, also your earths could be twisted together thus giving a good continuity, but have come away from the socket terminal
 
could a conductor have come lose between testing r1r2 and testing zs

im thinking of retesting the circuit from scratch as well has ze
 
If it's with an old socket then try inserting and withdrawing it a few times (to clean the contacts). Before restarting your test take the socket off and test at the rear of the socket and let us know your findings. It could also be a faulty socket.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Problem with zs test
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
18

Advert

Thread statistics

Created
coatesykid,
Last reply from
topquark,
Replies
18
Views
3,182

Advert

Back
Top