I have posted this before put dose not seem to of posted so sorry if is a repost I have added a few socket outlets to my ring main everything is working fine but for some reason when I have tested every socket with a socket tester some outlets read that L and N are swaped over only on a few sockets I have done the following

Tested tester to make sure it is not at fault
Unplugged everything

Can anyone tell me why is is happening and only on a few sockets


Thanks in advance
 
either you have wired some sockets reversed L and N or there is a reverse on an existing socket or a junction box.
 
I would suggest you carry out the correct continuity testing on the ring final circuit before energising and certainly before using a socket tester.

Continuity of ring final circuit conductors

Reason: This test ensures that all ring final circuits (sockets usually) are indeed a continuous ring with no interconnects or breaks within it.

Method: The line, neutral and earth conductors of the circuit are identified and a measurement from one end to the other end of each is taken. These results are r1, r2 and rn.
The incoming line conductor is then connected to the outgoing earth conductor and the outgoing line conductor is connected to the incoming earth conductor. A measurement is then taken at ALL socket outlets on the ring. This result is R1+R2 for that circuit. The above is then repeated using the neutral conductor instead of the earth conductor.
 
Last edited:
His profile says Trainee, skinney are you currently on any courses if so you may be better registering for the trainee section.
 
I have posted this before put dose not seem to of posted so sorry if is a repost I have added a few socket outlets to my ring main everything is working fine but for some reason when I have tested every socket with a socket tester some outlets read that L and N are swaped over only on a few sockets I have done the following

Tested tester to make sure it is not at fault
Unplugged everything

Can anyone tell me why is is happening and only on a few sockets Because there's a problem with those sockets.


Thanks in advance

Hope this helps.
 

Reply to problen with ring main in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
481
Hi all I would like to put some sockets in the attic and keep them on the main house ring main. Am I right in saying I can pull one of the legs...
Replies
1
Views
208
Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
Replies
2
Views
292
Hello, I need to run a mains spur off the existing ring main in a domestic property. To get the double socket to the correct place I have to drill...
Replies
3
Views
240
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
274

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock