if using 2 rods, they should be spaced 1.5 x the rod length.
 
might take 6 weeks though. Might be easier ter get the cheque by banging in Rods.

Whats this about black art I thought that was the spreads domain
 
Its a TT with a Ze of 207 , ( high i know ) what can i do about this ? inform dno :- convert to TNC-S?

Any way : PEFC : 1.11 a , ( LOW ) PSCC 1.2KA . HIGHEST Zs in house 3.43 , existing bonding 6mm .

As a rule of thumb ive heard of people using 0.5 of main supply tails : 16mm .

However if i inform the DNO of the high Ze and they convert to TNC-S , pefc will rise to eg: 230/0.35 : 657A min.

Any ideas ? or can show me how to do the adiabatic with this ?

I think you need to sit down with your calculator and revisit some of these sums and your testing..... if you have a Zs of 3.35 when you have a Ze of 207, then that means you have an R1R2 value of -203.65. Now that's a cable I'd really love to know where to buy.

The low pfc values that you get on TT installs are part of the reason for the requirements for RCD protection; it is realised that you will never get anywhere near disconnection times with that little current.

To lower your Ra then as others have said, bang in some nice LONG 5/8 rods down to at least a couple of metres.
 
Parallel paths with that bonding and all the CPC I would guess be the reason he as got a low Zs there RT

That was my first thought as well, but in which case you'd surely then expect a Pefc of around 50-70A based on those figures?! Although..... 1.11A x 230V = R255 = 207 + 48 (roughly). But then again, you wouldn't be getting r1r2 value of 48ohms..... So, methinks some double checking in the testing department might still pay dividends.

Happy to be proved wrong, it's just the numbers leapt at me straight away!!
 

Reply to pro's advice needed in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
473
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Hi Everyone, I'm new to this forum and am hoping someone can give me some advice, as I'm absolutely clueless when it comes to these things. I'm...
Replies
11
Views
2K
Morning all, Looking for some opinions MK Sentry Dual RCD 63/30 CU Fluke 1662 readings... 2 lead hi current Ze= 1.87 Ohms PEFC = 6A PSCC =...
Replies
12
Views
2K
Hi, First time posting on here so apologies if I'm missing any basic information, but hopefully someone can help me as an amateur DIY-er and...
Replies
10
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock