John-

-
Reaction score
48
Does anyone perform a prospective short circuit and, where no RCD / RCCBO, a prospective Fault Current test on the end of circuits on inspection and tests?

I get we do ZS, but how do we know that the CPC or Line conductors are man enough for fault currents of X duration?

S2K2 => I2 T?


Cheers

John
 
If the circuits are "standard" and it is fed from the usual style of MCB then they would meet the adiabatic limit.

Table B7 in the OSG has the limits based on the generic MCB standard and differing fault currents in terms of CPC size. Though even the 3kA one is more than you would typically see at the end of a final circuit.

Section 8.5.1 starting on page 98 of the IET's Electrical Installation Design Guide (4th edition) has more detail and includes example MCBs from MK & Hager that have lower let-through than the limits of the generic specification.

TL;DR using reputable T&E sized for the MCB is sufficient is end Zs met.
 
The max fault level at the end of the cable is largely irrelevant, the Zs/minimum fault level of course is vital to ensure the ocpd operates in time.

If we put a nice long cable run, there is no guarantee that when the user drives a nail between line and cpc they will bother walking that full distance to the far end to do it.

They will probably do it close to the consumer unit, therefore if you do check the adiabatic on the cables, you need to use the fault level from the start of the run, not the far end.

So say I have a Re of 0.08 ohm ( so around 2.7kA on min voltage - 3kA max), we need to make sure the cables survive for 3kA perspective through their ocpd, rather than just the 45A at the end of a long lighting circuit having a 5 ohm Zs, which is within the 6A rcbo/mcb limit.

The standard arrangements assume a maximum let-through of the main fuse limiting the damage, so providing you fit mcbs capable of handling that (usually 6kA), then the standard circuits in the standard, and osg can withstand the let through of these mcbs.

This might not be the case in industrial settings as the fault level may be higher, with substantially bigger fuses, and larger let through of the industrial mcbs.

Hence in these cases you do need to check the adiabatic for seemingly "standard circuits"
 
Slightly off topic but it amazes me how often within commercial applications design load currents have been factored around the ratings of say XLPE cables and then they wonder why the protective device mcb or mccb has tripped prematurely. Although these XLPEs can operate under higher temps, hence load currents. They fail to take into account the thermal affects of those cables and how they can affect time current characteristics of the protective device if its taken outside specified ambient operating temps. Another one is those type Ds replacing a C type without the circuit Zs limits being taken into consideration. As said often overlooked ?
 
BS7909 does both PFCs and EFLI at the furthest point from the distro gear for safety reasons (ensuring sufficient impedance and fault currents to operate the protective device, and helps confirm volt drop too.
 

Reply to Prospective fault at the end of circuits in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
763
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
hi in college and watched some YouTube videos and read up on things I think I got the right formula but I'm not sure. Zsc= Zesc(or Zdbsc) +...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock