Hi
Interesting thread, PV is not an area im involved in but i would like to know more.
It seems to me that the PV supply needs to be connected upstream of all final circuits, connection made via a CPD.
With regards to a RCD on the PV ac supply, providing the inverter has simple seperation, where is the earth reference for the RCD?
Cheers
I know next to nothing about PV, but sources of supply are all basically the same.
That's one of the things I want to know, do all inverters have outputs which are electrically separate from Earth?
Well you can earth the d.c side of the inverter providing the inverter has seperation.
Now the seperation is there to stop d.c current feeding onto the a.c side. Now where simple seperation is not provided by the inverter then a type b rcd needs to be installed.
Cheers
LV 3 phase inverters.
In particular the ABB Trio range.
Although there are separate connections for each phase, neutral and earth, the earth and neutral are connected together internally.
In fact it appears that the neutral is nothing more than another earth conductor, as there is no internal connection from the neutral to any other part of the inverter.
Hi
Im not able to coment on abb trio, unless you can give an explanation?
This unit has no seperation, so requires RCM, secondly it will require a type B RCD on the a.c outlet, so no seperation d.c to a.c.
Cheers
What's to explain?
Earth and neutral are connected together at the inverter.
Don't know what you mean by seperation and needing an RCM?
Why would it require an RCD?
Would existing RCDs (if there are any) in the installation, require changing from A/AC to B type?
What's to explain?
RCM - residual current monitor.
The type b RCD would be needed between the inverter and the final circuits as it will operate in the event of DC residual currents flowing due to the lack of DC/AC separation in the inverter.
All normal RCDs in the installation can remain as they are, the type b will disconnect the source of the DC (inverter)
Normal RCDs are prevented from operating by DC as it saturates the core balance transformer, which is one method used to prevent RCDs tripping during EFLI testing
Why is an RCD required between the inverter and final circuits?
Inverter is connected to the incoming supply from the grid via SY cable through trunking to a meter then to an isolator , then to fuses (can't remember the ratings) then via SWA to to a busbar chamber in the intake room.
Not sure if there is d.c./AC separation at the inverter, though there is an indicator led for if there is an earth fault on the d.c. side?
I have to say this is a really interesting thread!
if we need to disconnect both ends, how about this.
from the main db, circuit starts with an RCBO, then connected to that would be a 6A MCB on a shunt and that circuit holds open a NO contactor which the inverter end is connected to (the one that runs back to the main db).
so by doing this, should there be overload or earth fault on that circuit, thevRCBO will trip and disconnect the line at the board end and open the contactor disconnecting both line and neutral from the inverter. But would this disconnect or open the contactor in the right time to comply?
Just a thought?? No idea if it would be ok or not
Hi
Without simple seperation between d.c and a.c, a fault on dc could transfer to the a.c side, so a type B RCD must be installed.
Cheers
What's to explain?
Hi
How you know the N-E link is internal and its purpose?
Cheers
As far as I am aware, these particular inverters do not require type B RCDs.
I know that the earth and neutral are linked by visual inspection.
I was interested in why there is a neutral for 3 phase inverters, when to my mind there would be no need, as there is no transformer to connect a neutral to the star point.
As no one I asked could provide an answer as to whether a neutral is required, I thought I would investigate the next inverter I got hold of.
There is a wiring block to connect the output conductors, then some short lengths of conductors to over voltage surge arresters, with blank modules for the earth and neutral, the other side of the surge arresters, is where the earth and neutral are linked, with only the earth and phase conductors continuing into the innards of the inverter.
Something that puzzles me, is how the inverter knows there is a connection to the grid?
Does the inverter pause the output from the inverter to measure the grid, or is there some manner that the inverter can differentiate between the grid voltage and the inverter voltage?
How is a 6A MCB with a shunt trip going to hold a contractor open?
It is required if the inverter does not provide suitable separation between the DC and AC.
The basic outline of the theory is that if DC can get into the AC circuit then it will prevent a A or AC RCD from operating as the DC saturates the sensing coils these preventing the RCD from operating.
Injecting DC into an AC RCD is one method which can be used in 'anti-trip' Zs testing to prevent an RCD from tripping.
I'd be surprised if a non-domestic unit wasn't provided with appropriate separation, but it really isn't my field so I don't know.
Seems a bit complicated when just two RCDs will suffice.
Two RCDs are unlikely to suffice, but we've strayed so far in this topic I'm not certain what you are saying the two RCDs would doing?
This started with the provision of 30mA RCD protection to a PV inverter circuit (in a domestic setup if that makes any odds) in a situation where regs require it for the usual shock protection reasons. But now it's strayed into type B RCDs and N-E links so I'm getting a little lost!
If the cable from the inverter to the mains requires RCD protection as you said because it may be concealed in a wall less than 50mm.
Then two RCDs, one at each end of the cable would suffice.
One will disconnect the power from the inverter, and the other the power from the mains.
I mentioned the fact that the neutral and earth are linked because someone asked if all inverters are separated from earth.
Two RCDs may not suffice, if the inverter is earth referenced through a solid link then it should work, but if it's earth referenced through a resistance or through fortuitous connection it may not.
The bottom line that most of us were getting at is that the circuit should be designed so that RCD protection is not required, which isn't exactly difficult really.
Hi
Im lost, whats this disconnect both ends about? The inverter must disconect within 5 secs, as we cant connect to Final circuit the a Distribution circuit it is, 5 Sec disconection.
Cheers
Even if it's on an MCB you will still have the issue of two supplies.
Hi
Cheers
but if you create an earth fault or even dead short or whatever, the PV could still be feeding the circuit that you should hope would be dead.
It it will hold it closed sorry, then when triggered it will release the contactor and shut the PV end off.
You don't actually know what a shunt trip is do you?
A shunt trip is a unit which you can fit to an MCB to allow it to be tripped by a remote signal. They can be used to add RCD protection to larger mcbs or mccbs/acbs by using an earth leakage relay connects to a shunt trip to operate the breaker.
This is why I suggested that a DP MCB at the inverter fitted with a shunt trip which is operated by an auxiliary contact on the RCD at the CU end might provide adequate protection.
Hi
Cheers
It came up as a result of the mention of a PV circuit being provided with RCD protection.
I suggested the only way a PV circuit which requires 30mA RCD could be provided with it is if the RCD disconnects both ends of the supply.
But I thought it would illustrate why a PV circuit should be designed to not need RCD protection,
I didn't mean a shunt, I mean one of those things you use to fix an indicator to an MCB for example, I can't think what they are called, I call them a shunt, it's probably not but Hager do them anyway.
Don't see why an RCD would be affected by the inverter being referenced to earth?
Difficult, I'd say virtually impossible with a TT installation.
Hi
All inverters with no simple seperation require RCD type b protection.
I can only assume the inverter reacts the same as a tx, three phase unbalanced load, neutral current, connecting the neutral to earth to tie star point down etc.
The inverter will need to synchronise with the grid voltage, id assume at this point it can differentiate.
Cheers
Hi
Only one rcd would be required at teh output of the Inverter.
Cheers
Not for a fault in the cable between the inverter and mains.
As has already been posted, if an RCD were to cut the power from the inverter, it would leave the power from the mains connected.
There would need to be one at each end of the cable, one for the mains and one for the inverter.
There's a multitude of devices which can be added to breakers to perform any function you want
If the inverter N is solidly referenced to E then the RCD will work. If the inverter N is not referenced to earth then the RCD is unnecessary as you have an electrically separate supply so it cannot deliver a shock.
But what if there is a N-E link which is fortuitous?
(I don't know the answer and am probably overthinking now)
In a TT you would still want to design the circuit to not need 30mA RCD, only the fault protection RCD which is likely to required, and ensure that the inverter used does not include a N-E link so providing a n electrically separate supply when not connected to the grid.
In theory (and yes it is an unconomical and borederline daft theory) you could avoid any RCD protection completely by using double insulation as the protective measure for the circuit instead of ADS, or even electrical separation. Or of course by getting the Ra low enough to not require RCD
Just in city's at the mo and flicking through the PE magazine and napit have just written an article on this and says the rcd must be located at the inverter end. Page 37 of Febs PE magazine if any ones interested.
Now we're going to get even more confused lol :)
But then the grid supply would not be disconnected in the event of a fault.
This is a cable with a source of supply at both ends.
Hi
Im not sure i follow, so lets break things down.
We must not connect to final circuits, so 5 Sec rule applys.
If there is no seperation on the inverter or the PV cable a.c requires rcd prorection then this is placed at the inverter.
Unlike a tx the inverter is not connected to the general mass of earth at the star point.
The PV a.c cable needs to be provided with fault protetcion at the connection to the mains a.c.
If a fault occurs on the a.c system, the power will disconnect within 5 secs, the loss of power will shut the inverter down in milliseconds.
If a fault on the PV cable occurs then the RCD at the inverter operates, thus causing loss of power and inverter shuting down.
If we look at ADS and earting the TX is earthed, so contact with live parts and general mass of earth will give rise to a risk of shock, this isnt the case with the inverter.
Cheers
Pv on rcd
gnselectricals,
Deleted member 26818,