E
Engineer54
coupled together.
Good to hear that, it wasn't clear in your earlier post!! lol!! So why was it hard, was you using a hammer?? You daft fool ...lol!! A good SDS drill should have made things much easier, you can purchase the driving tool to fit an SDS, or make one up yourself!! So did you link the existing earth rod to your new driven system as i suggested?? I tend to forget to mention that it is Always good to install a concrete or heavy Plastic earth pit over the rod and connection. One, it protects the connection and secondly the rod position doesn't get lost over time...
But well done, an Ra of 42ohms is darned better than 126 ohms, and it will keep improving over the next year or two as the ground consolidates around the rod. Don't be too surprised to see as much as a 10 to 15% improvement, it'll certainly be a sub 40 ohms figure anyway!!