Discuss R2 testing necessary for an eicr certificate. in the UK Electrical Forum area at ElectriciansForums.net
No. They are both methods of verifying the same thing. They are an either/or in any situation, periodic inspection or initial verification.
Worrying question from someone carrying out periodic inspections to be honest.
I only asked because im making my eicr certificate and got my assesment coming this saturday.
Just wanted to make sure the inspector wont say anything when i put n/a
Consider as well that it is not always necessary to carry out R1+R2 tests for an EICR. R1+R2 is intended as initial verification prior to energising, as a circuit is already energised then it could be considered redundant. A sensible approach is to carry out R1+R2 tests on an unknown installation with no previous certification available. If a previous EIC or EICR is available then a Zs test is sufficient and compare the result to the previous cert, if the result is identical or close it may be assumed R1+R2 is also satisfactory. R2 tests are useful on lighting circuits with fancy class 1 lights which cannot easily be dropped to access terminations.
You should also get your terminology correct, there is no r1+r2 test, it is R1+R2.
r1 and r2 are ring circuit end to end readings.
These test are carried out an a new instalation. I wantrd to ask what i should regarding the main supply overcurrent protective devise as it is sealed and not visable is it ok to put limitaion or should i contact uk power to find out ?
Might not be seeing the picture right. Looks like a resin sealed head to me. Are you saying it is a hinged cast enclosure that is wire sealed ?
I beleve so as i forgot to check the writing on the enclosure. Will go back in a few days to check if it has any fure rating written on it
Yeah, that's a WT Henley ironclad service cutout (ISCO) with an ironclad sealing chamber beneath.
Originally it would have been double pole fused, but hopefully someone has put a solid link in the neutral by now!
New posts
Reply to R2 testing necessary for an eicr certificate. in the UK Electrical Forum area at ElectriciansForums.net
Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
OLDBOY
O
Hi, recently had an EICR test done by 'Landlord Certificates' which failed due to circuite 3 having two radial circuits into a single 32amp MCB...
4K
Hi guys Completed an EICR yesterday. One of the Sockets Radials had no CPC so R1+R2 plus Zs could not be not be completed. Does anyone know the...
On a Eicr on agreed limations of iinpections what do you normally put And what percentage do you test at..
Hi guys, need a bit of advice, EICR was completed on the property which needed a new consumer unit and a few other bits like broken sockets and...