Is it necessary to do the r2 test if you have done r1+ r2 test for an eicr certificate
Discuss R2 testing necessary for an eicr certificate. in the UK Electrical Forum area at ElectriciansForums.net
I only asked because im making my eicr certificate and got my assesment coming this saturday.No. They are both methods of verifying the same thing. They are an either/or in any situation, periodic inspection or initial verification.
Worrying question from someone carrying out periodic inspections to be honest.
Sorry i mean eicWhy EICR if it's a new installation ?
These test are carried out an a new instalation. I wantrd to ask what i should regarding the main supply overcurrent protective devise as it is sealed and not visable is it ok to put limitaion or should i contact uk power to find out ?
View attachment 38634
The one where the main armoured cable is coming into.Ummm .. what main fuse ?
The one where the main armoured cable is coming into.
I beleve so as i forgot to check the writing on the enclosure. Will go back in a few days to check if it has any fure rating written on itMight not be seeing the picture right. Looks like a resin sealed head to me. Are you saying it is a hinged cast enclosure that is wire sealed ?
The DIY sheath connection on the incomer for a kick off. Did you put that in ?WhT would yoy recommend changing
Might not be seeing the picture right. Looks like a resin sealed head to me. Are you saying it is a hinged cast enclosure that is wire sealed ?