May 28, 2020
20
Cumbernauld
Guys needvadvice please
I was asked to carry out an annual inspction of a DB recently
There are 12 in number radial circuits suppling sockets wired in 4mm singles protected by 32A mcb the cables are enclosed in metal trunking and supply 13a socket outlets , are the mcbs now overated as the cables are now rated at 28A maximum due to the wiring method and should I also be fitting rcbos as the installationis is classed as unsupervised
It is a large office and the socets are for IT equipment my intention are to downrate the mcb or rcbo to 25A if they are available.
Thanks Dimspark
Reactions: westward10
Thanks Dimspark
Check table 4D1A.
Ref method B.
2 cables, single phase 😀
Check table 4D1A.
Ref method B.
Dimspark by name need to get new glasses had to ask the question as on other sites a subby is swapping out 32A for 25A breakers and are also 4mm single phase and I was asked to do this particular board because it had been missed and no report has been produced I do feel like a Dimspark now
Thanks for the reply HappyHippyDad
Thanks Pretty Mouth
Check table 4D1A.
Ref method B.
Cumbernauld
Radial Circuits Wired in 4mm and 32A MCB
UK
Dimspark,
Dimspark,