@chris301up you may understand the need for isolation, but do you have the knowledge and tools to practice safe isolation?
The existing 6mm cable is already 20m long, have you referenced BS7671 to check suitability of the new extended length in 6mm, taking account of installation method, rating factors, voltage drop, and maximum earth fault loop impedance to meet required CPD disconnection times, for the design current?
Please call a sparky in before you hurt yourself, or someone else.